De-rating - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 05-18-2010, 12:57 PM   #16
Master Electrician
Rewards Points: 5,082
It's okay to derate #12 from 30 amps in the table. It is not okay to place #12 on a 30 amp breaker except in special HVAC and motor circuits. #12 is still limited to 20 amp breaker.
brric is offline   Reply With Quote
Old 05-18-2010, 01:49 PM   #17
Sparkaholic
Rewards Points: 150
Send a message via Yahoo to sparks1up
One more factor to consider is distance! Especially for that switch loop. The garage is powered from the house and the light (on the garage) must be powered from the garage and switched from the house so that means the wiring for the light has to travel 3 times the total distance (from house panel to garage, back to the switch in house, then back to light on garage)
How far is the garage from the house?
Also the switch loop is the same wire coming and going carrying the same current and in really should NOT be counted twice as a current carrying conductor. Some inspector's might not agree so correct me if I am wrong! But if you do please tell me where in the code it says different.
Answers based on the mood I am in when you ask!
sparks1up is offline   Reply With Quote
Ceramic tile PEI rating - is this store manager trying to scam me? megs1082 Flooring 9 03-20-2011 05:03 PM
Compressor cfm rating required for framing nailer tmeehan Tools 8 05-01-2009 11:17 AM
Receptacle Rating question Ultrarunner2017 Electrical 19 12-20-2008 06:20 PM
Receptacle Rating question Ultrarunner2017 Electrical 5 12-18-2008 05:36 PM
How do panels get their amperage rating? Randell Tarin Electrical 14 01-23-2008 06:10 PM