Conduit Wire - Electrical - DIY Chatroom Home Improvement Forum
Like Tree4Likes
  • 3 Post By rjniles
  • 1 Post By Oso954
Old 08-29-2019, 10:12 AM   #1
Rewards Points: 56
Conduit Wire
When installing wire in a short section of pvc conduit above ground (like to an outside sub-panel with UF wire) is it permissible to strip the wire's sheathing back the same length as the conduit and then install it? Or is this not advisable since the ground wire would be exposed/unprotected along the length of the pvc conduit?
CommanderDave is offline   Reply With Quote
Old 08-29-2019, 10:37 AM   #2
jproffer's Avatar
Rewards Points: 596
Re: Conduit Wire
Not sure about code, etc, but if you use a fitting on the end of the conduit that would hold the cable (similar to a romex clamp in a panel), then I would be comfortable with it. Someone more code knowledgeable than I will be along to discuss that side of it.
jproffer is online now   Reply With Quote
Old 08-29-2019, 10:49 AM   #3
A "Handy Husband"
rjniles's Avatar
Rewards Points: 970
Re: Conduit Wire
Stripping the jacket off a listed cable assembly in a conduit is a code violation.
Sent from my Moto E (4) Plus using Tapatalk
jbfan, jproffer and jhil like this.
My electrical answers are based on 2017 NEC, you may have local amendments.
rjniles is offline   Reply With Quote
Old 08-29-2019, 04:29 PM   #4
Rewards Points: 56
Re: Conduit Wire
I believe the 2017 NEC Chapter 9 Tables Note 9 states that it is permissible...."assemblies of single insulated conductors without an overall covering are not considered as a cable when determining conduit or tubing fill area. The conduit or tubing fill for the assemblies is calculated based upon the individual conductors." But then I may not be smart enough to figure out what this is really saying.
Old 08-29-2019, 05:37 PM   #5
Oso954's Avatar
Rewards Points: 2,080
Re: Conduit Wire
I read that as triplex or quadruplex cables, etc, (typically twisted wire cable assemblies) are calculated on wire size only, as they have no jacket. It does not say that you can strip a jacketed cable assembly to save on conduit fill.
If you are having fill problems, upsize your conduit.
jhil likes this.
Oso954 is offline   Reply With Quote
Old 08-29-2019, 06:50 PM   #6
Rewards Points: 88
Re: Conduit Wire
I seem to recall the NEC 2010 had a beef about that when the Type NM cable's sheath jacket is removed, the required "ID labeling" of the conductors was removed.
I think the NEC 2010 wanted at least a I/4 in. of the Type NM jacket protruding passed the end of the conduit nipple, to prove the NM sheath jacket was still intact.
The NEC 2017 may have revised this old ruling though. But I am not going to order me a NEC 2017 for 90 bucks, just to find out though.
Gregsoldtruck79 is offline   Reply With Quote
Tags
conduit , pvc , wire