Conduit Question - Electrical - DIY Chatroom Home Improvement Forum
Like Tree1Likes
  • 1 Post By MrElectricianTV
Old 06-13-2019, 12:55 AM   #1
Question
Conduit Question
Quick question (probably a dumb one)
I wanted to add outlets to my unfinished basement. Block walls, open floor joist, with no plans of ever finishing them.
I plan on running 12/2 (from the breaker box) through the open floor joist, over to the wall, down a vertical piece of conduit then connect it to a handy box
My question is how far from the ceiling does my conduit need to be?
I'm aware that I should use conduit bushings to protect the wire at the open end. I plan on using a GFI outlet.
bigben662 is offline   Reply With Quote
Old 06-13-2019, 05:34 AM   #2
Very Stable Genius
CodeMatters's Avatar
Rewards Points: 8,160
Re: Conduit Question
Your location will likely change the answer. Consider adding that to your profile.
Up here the CEC/OESC requires some form of mechanical protection for NM
cable on surface at heights below 1.5m.
Code ref: 12-518
CodeMatters is offline   Reply With Quote
The Following User Says Thank You to CodeMatters For This Useful Post:
bigben662 (06-13-2019)
Old 06-13-2019, 07:57 AM   #3
Rewards Points: 18
I do that in my rental properties using plastic conduit running down to a square box. I usually have the conduit run down starting at a point between the 1st floor joists where that is possibke. Where there is a joist directly above where I need to run the conduit, I drop the conduit an inch or so below the joist, and start there.
I am no expert on code, but I believe that all basement receptacles need to be GFCI protected.
Sent from my SM-G530T using Tapatalk
jeffmattero76 is offline   Reply With Quote
The Following User Says Thank You to jeffmattero76 For This Useful Post:
Old 06-13-2019, 08:27 AM   #4
Rewards Points: 12
Corollary: is there a minimum distance from the floor that the conduit needs to be?
huesmann is online now   Reply With Quote
Old 06-13-2019, 08:57 AM   #5
Rewards Points: 18
Again, not a code expert, but I don't believe there is any "distance from the floor" requirement in the code.
Old 06-13-2019, 09:04 AM   #6
Rewards Points: 2,084
I plan on running 12/2 (from the breaker box) through the open floor joist, over to the wall, down a vertical piece of conduit then connect it to a handy box. You should use 4" square boxes.
My question is how far from the ceiling does my conduit need to be? I don't know of any such requirement. I would let it poke above the bottom of the ceiling joist a little.
I'm aware that I should use conduit bushings to protect the wire at the open end. I plan on using a GFI outlet. You need a connector at the entrance of the conduit to prevent the cable from being pulled out. There are EMT to Romex changeover connectors for this.
Be sure to get a permit and have the work inspected.
John Grabowski
MrElectrician.TV
MrElectricianTV is offline   Reply With Quote
The Following User Says Thank You to MrElectricianTV For This Useful Post:
Old 06-13-2019, 10:25 AM   #7
I'm with you on your all your foot notes except the first one. Is 4" boxes code, or your personal preference?
Old 06-13-2019, 10:44 AM   #8
By code 2.25 cubic inches are required for each #12 conductor. A wiring device such as an outlet, switch, or GFCI takes up the space of two conductors. All grounds can be connected and only account for one conductor. So with one 12/2 and a GFCI you need space for at least 5 conductors. So you need at least 11.25 cubic inches. With two 12/2 Romex's you will have 7 conductors (15.75 cubic inches). A clamp inside the box also counts as one conductor. It is also easier to work when you have extra room.
Also, another reason why I suggested 4" square boxes. If you do decide to finish the walls at some time in the future, you can use mud rings to extend out to the finished wall without having to move or change the electrical boxes. You could even use mud rings now without the finished wall.
I tend to use 4" x 4" x 2 1/8" for comfort and room for future wires.
bigben662 likes this.
John Grabowski
MrElectrician.TV
Old 06-13-2019, 10:45 AM   #9
Electrical Contractor
jbfan's Avatar
Rewards Points: 6,940
Not code, but will look much better and give you more room.
Yes I am a pirate, two hundred years too late
The cannons don't thunder, there's nothing to plunder
I'm an over-forty victim of fate.
jbfan is online now   Reply With Quote
The Following User Says Thank You to jbfan For This Useful Post: