I have purchased a commercial grade convection oven for my home because I run a baking business from my kitchen. Here is the plate information:
230 Volts
53 Amps
Single Phase or 3-Phase wiring (planning on single phase of course)
All of my other major appliances are gas, but even still I don't have enough wattage left in my 100AMP panel box so I am upgrading it to a 200AMP service.
My question: I am planning on using a 60AMP breaker to carry this thing, and although I know 6 Gauge wire is used for this amperage, should I be using 6/2? or should I be using 6 Gauge THHN wire? The run is less than 75 feet.
rlineberg is offline   Reply With Quote
Old 05-07-2010, 08:58 AM   #2
Sparkaholic
Rewards Points: 150
Send a message via Yahoo to sparks1up
#6 gauge romex is only good for 55-amps so you cannot connect to a 60-amp breaker. Also assuming you did use romex it would have to be a 6-3 with ground (4 wires).
sparks1up is offline   Reply With Quote
Old 05-07-2010, 10:04 AM   #3
Electrician
Rewards Points: 908
Is the 53A for single phase or when it is wired to 3 phase.
Also you say this is for a bakeing business you have in your house, how long will this stove be running. Does it go all day or a couple hrs a day. The reason I ask if it is used all day you will have to consider it a contoinus load which means you will have to derate it by 80%. I am assumeing the NEC is the same when it comes to continous loads to what the CEC says.
This would take you to 53/.8=66A. So now your looking at #4(based on CEC may be different in the NEC) and a 70A breaker.
darren is offline   Reply With Quote
Old 05-07-2010, 10:04 AM   #4
I have not run the wire yet, but is sounds like I will want to use the 6 Gauge THHN. Is this correct?
Old 05-07-2010, 10:05 AM   #5
Actually you are allowed to upgrade to the next highest breaker
So long as the anticipated load does not exceed the wire rating
THHN has a higher rating -65a & I would use that
A 4 wire feed is required
Darren brings up a good point
Old 05-07-2010, 10:08 AM   #6
Electrical Contractor
kbsparky's Avatar
4-wire feed is not required on an appliance with a 240 volt only rating. Only if it is rated 120/240 volts would a neutral conductor be needed. It appears this is not the case in this instance.
As for the wire size and circuit breaker, the #6 is rated for 55 Amps. Since the nameplate requires 53 Amps, that is within tolerance. You are allowed to use the next-size standard breaker, which is 60 Amp.
Such an appliance would have to be direct-wired in most cases.
-KB
Old 05-07-2010, 10:12 AM   #7
Ah, Thanks - I'm used to stove requiring 120/240 w/controls
Old 05-07-2010, 10:13 AM   #8
Sparkaholic
Rewards Points: 150
Darren makes a good point! I typically size my wiring to 125% of the load for continuous loads which works out about the same (53 x 1.25 = 66.25-amps) = #4 wire)
Old 05-07-2010, 10:19 AM   #9
Good questions...
The 53A is when it is wired for single phase. (I believe the 3-phase is like 32-ish, but not 100% sure)
The max use of this oven is 2-3 days per week, 4 hours at a time.
Is the #4 copper or aluminum? And should it be THHN?
Old 05-07-2010, 10:23 AM   #10
Interesting thought
Cooking a big turkey can take longer then 3 hours
So do you always upsize the wire just for that one day ?
Old 05-07-2010, 10:25 AM   #11
kbsparky's Avatar
Ovens are not continuous loads. You would burn up anything cooking in there if the elements were on full blast for more than 3 hours....
-KB
Old 05-07-2010, 10:27 AM   #12
This is true, but I don't keep the same bread in the oven for the 3 hours. It is a series of bread pans for about 45 minutes each. So the oven does not get turned off in between.
Old 05-07-2010, 10:28 AM   #13
That's true....so #4 wire is not needed
If you will be cooking for 4 hours I hope you have a good exhaust fan to get the heat out of the house in the summer
Old 05-07-2010, 10:35 AM   #14
I am pretty sure I don't have the connections for a 4 wire feed. It is indeed a 240 volt rating only. I only have 2 lugs in the oven itself and of course a ground.
I see what you are saying about about the 53A nameplate rating... but this continuous load thing has me thinking of of kicking it up a notch just to be safe. I never bake anything at the full 500 degrees though, so I don't think I would ever touch that 53A. What are your thoughts?
Old 05-07-2010, 11:09 AM   #15
kbsparky's Avatar
Any oven on a normal "Bake" setting cycles on and off to maintain the temperature. This is not a "continuous" load.
-KB
SCARY oven fire! Why did it burn? Beth777 Appliances 73 09-03-2016 02:19 PM
Oven Blew Up at Connector with Element cynthiap Appliances 6 10-31-2015 09:48 AM
installing ge profile convection oven momof2labs Kitchen & Bath Remodeling 1 02-27-2010 01:43 PM
Gas oven problems gregsmy Appliances 1 12-03-2009 05:55 AM
Counter top trim to fit with slide in oven bhagey Appliances 1 07-17-2009 08:32 AM