I am running a 125Amp sub-panel off of my 200amp main panel with 1/0-1/0-1/0 Aluminum SER Cable w/ 2AWG Ground. 1st question is will that wire meet code for the correct size and second is this sub-panel is in a slab poured addition and I would like to to run it in the attic to get to the main panel. Can I run it exposed or does it have to be protected with PVC? I think in the walls it just has to be 1.25 inches away from the edge but i could be wrong with that. Is this more of a question i would need to call my local inspector for?
DaleMN is offline   Reply With Quote
Old 07-24-2017, 03:21 PM   #2
Master Electrician
Rewards Points: 5,076
Re: Code for SER in Attic Space
Exposed in the attic is fine. Derating would be required if the cable is buried in insulation.
DaleMN likes this.
brric is online now   Reply With Quote
The Following User Says Thank You to brric For This Useful Post:
DaleMN (07-25-2017)
Old 07-26-2017, 01:04 AM   #3
Disrespectful to dirt
Fishbulb28's Avatar
Rewards Points: 2,002
No, 1/0 aluminum is only rated at best for 120 amps and thus is too small. It used to be suitable for 125 amp feeders in residential uses but no longer. Somehow it magically became unsafe for feeders such as this but safe for carrying the same load in a different setting. Grrr.
What size you need depends on what version of the NEC your area is using and whether or not this cable runs through insulation in the attic.
If you are running through insulation AND using the 2011 or 2014 NEC, the cable is derated as brric pointed out. You're stuck using the 60C ampacity column in the table. You will need 3/0 aluminum.
If you're not running through insulation, or running through insulation and using the 2017 NEC, only 2/0 is needed.
You may also need larger cable after derating for ambient temperature. What's the highest temperature the attic sustains in hot weather?
Are you running the cable on top of the joists or drilling to go through them? If on top, you may need to protect the cable. Does this attic have a permanently mounted ladder or stairs? If so, you'll need protection for the cable's entire run up there. Wood guard strips at least as high as the cable are fine. If no ladder or stairs, protection is only needed within 6' of the opening.
You are correct. It can make installing cable interesting when using larger diameter cables in 2x4 framed walls.
Fishbulb28 is online now   Reply With Quote
Old 07-26-2017, 06:56 AM   #4
Electrical Contractor
jbfan's Avatar
Rewards Points: 932
Chances are he can not put a 125 amp breaker in his main panel anyway.
Yes I am a pirate, two hundred years too late
The cannons don't thunder, there's nothing to plunder
I'm an over-forty victim of fate.
The Following User Says Thank You to jbfan For This Useful Post:
Jim Port (08-16-2017)
Old 07-26-2017, 09:30 AM   #5
A "Handy Husband"
rjniles's Avatar
Rewards Points: 686
+1
Use a 100 amp breaker in the main even if the sub and sub panel breaker are 125 amps.
DaleMN likes this.
Old 08-16-2017, 12:02 PM   #6
Rewards Points: 14
I do have a 125amp breaker installed in my main breaker.
Old 08-16-2017, 12:18 PM   #7
A "Handy Husband"
rjniles's Avatar
Rewards Points: 686
Is your main panel rated to use a 125 amp breaker. Likely exceeds the stab rating of the panel. Change to 100 amp to meet the rating of the SER cable.
Sent from my RCT6203W46 using Tapatalk
My electrical answers are based on 2014 NEC, you may have local amendments.
The Following User Says Thank You to rjniles For This Useful Post:
DaleMN (08-16-2017)
Old 08-16-2017, 01:12 PM   #8
Rewards Points: 14
K will do. Thank.
Tags
125 , attic , pvc , ser
Ideal roof pitch for attic living space PixelPaul Building & Construction 8 06-23-2014 07:46 AM
Metal outlet box in attic space grounding BlueBSH Electrical 3 11-03-2012 05:27 PM
wiring code w.r.t. NEW folding stairs in garage attic fredsterl Electrical 4 09-25-2009 11:05 PM
Remodeling Attic Space befrenchy Building & Construction 4 09-21-2009 07:06 PM
What are the 'code' space requirements for a toilet in a three walled area?? 4just1don General DIY Discussions 6 05-21-2009 09:40 PM