Cable Size For 12VDC Application - Electrical - DIY Chatroom Home Improvement Forum
Old 07-01-2013, 05:40 AM   #1
Rewards Points: 1,356
cable size for 12VDC application
Hello
I am installing a backup sump pump (12VDC) in my basement
I was given (yes, given ...) 2 brand new deep cycle YUASA batteries (38Ah each)
I will interconnect them in parallel
The pump draws 20A peak, and ~10Amp continuous
I was thinking to use 10AWG? Is it OK, or should I go up to 8AWG?
french_guy is offline   Reply With Quote
Old 07-01-2013, 05:50 AM   #2
A "Handy Husband"
rjniles's Avatar
Rewards Points: 904
No reason not to use #12
My electrical answers are based on 2017 NEC, you may have local amendments.
rjniles is offline   Reply With Quote
Old 07-01-2013, 05:56 AM   #3
AWG12 is enough?
Old 07-01-2013, 07:17 AM   #4
A "Handy Husband"
rjniles's Avatar
Rewards Points: 904
Originally Posted by french_guy View Post
AWG12 is enough?
#12 is good for 20 amps at 120 volts or 12 volts. I assume the batteries will only be a short distance from the pump
Old 07-01-2013, 08:07 AM   #5
Rewards Points: 6,652
#12 stranded. They actually make harnesses that allow you to quick connect/disconnect, that you keep one end on the battery, and the other on the pump. Then you can swap out a set while the other set is charging on say your car or truck.
They also make Solar trickle chargers that can act as backup on house power.
Old 07-01-2013, 03:40 PM   #6
Oso954's Avatar
Rewards Points: 1,910
With a 10 amp load, you are going to have about 30 minutes of pumping time per battery, or about an hour with the pair. Depending on the scenario you are looking at, that may not take you through the power outage.
Oso954 is online now   Reply With Quote
Old 07-01-2013, 03:51 PM   #7
Yes, but it's better than nothing.......
Old 07-02-2013, 01:57 PM   #8
How did you come up to these values?
2 batteries in // will represent 76Ah, meaning the battery can deliver (theoritically) 76 Amps for 1 hour
So with a pump drawing 10 Amps, I should be fine for....7,5 hours of running time. How did you calculate 30 min or 1 hour?
The Following User Says Thank You to french_guy For This Useful Post:
mpoulton (07-02-2013)
Old 07-02-2013, 05:04 PM   #9
Oso954's Avatar
I didn’t calculate it, I pulled it off of a not so clear battery chart from a vendors site. But in doing so, I did make several mistakes, and for that I apologize. My biggest error was reading a 1Ca curve as a 10amp curve for the specific battery
So, you should get about 3 hours from one battery, and about double that with two, before making other adjustments that would reduce those times. To refine the numbers, we would need to know the voltage where the gpm drops off on the pump. I used the 10V mark on the chart. If the gpm starts dropping off seriously at 11V that would have to be adjusted for.
The numbers from the chart are also based on 77 degrees and should be temperature adjusted.
So, you are much better off than the numbers I originally posted. Again, I will apologize for that, and for not catching the error myself. But my intent was to flag that you cannot divide 76 by 10 and say I have 7.6 hours. You have 6 hours of pumping at best, and probably less.
Old 07-02-2013, 05:14 PM   #10
Roofmaster
Rewards Points: 2,220
Isnt 10 amps a heck of a lot for a sump pump to pull? What is this pump like 1.5 HP? That seems very high for a sump pump, does it not?
Old 07-02-2013, 05:31 PM   #11
Oso954's Avatar
120 watts, at 12VDC.
The Following User Says Thank You to Oso954 For This Useful Post:
Handyncheap (07-02-2013)
Old 07-02-2013, 06:46 PM   #12
Rewards Points: 1,192
Then you have the answers to your own question, ????
bobelectric is offline   Reply With Quote
Old 07-02-2013, 07:29 PM   #13
Civil Engineer
Rewards Points: 5,246
10A x 12V = 120 watts, as previously noted. A 120 watt pump is about 1/6HP, which is a very small pump. If the pump is say 80% efficient, the actual brake horsepower is perhaps 1/8 HP, which isn't going to pump much water, or pull much head.
Old 07-02-2013, 11:00 PM   #14
Engineer
Rewards Points: 161
Just remember that a device at a given wattage will draw 10 times more amperage at 12VDC than 120VAC.
120 Watts @ 120VAC = 1 Amp
120 Watts @ 12VDC = 10 Amps
diystephen is offline   Reply With Quote
Old 07-03-2013, 02:01 AM   #15
Wire Chewer
Red Squirrel's Avatar
Rewards Points: 584
Given battery cables are available in rather limited gauges and are usually for automotive uses, I'd just go with 4awg which is going to be the easiest to find. It's going to be more than enough.
Also to get more capacity I'd go with a couple deep cycle marine batteries. They are usually 100ah and cost a bit over 100 bucks. You'll also want to monitor the voltage and hydrogen levels to ensure the charger is operating properly.
Adequate Cable Size? bradmelnyk Electrical 7 09-01-2011 11:43 PM
Installation of Thermal Cable RenoMom Flooring 1 07-18-2011 09:45 PM
Inside Walls Cable Fishing/Routing tk3000 Building & Construction 9 07-05-2011 08:15 AM
Need Advice Old Metal NM Cable Anchors bltglt507 Electrical 15 12-18-2009 04:31 PM
Cable size advise needed makulos Electrical 3 10-22-2008 11:13 AM