Old 06-24-2009, 09:00 PM   #16
Originally Posted by DaleB View Post
PS- the wire is 8/3 or 6/3 direct burial from the panel- that's what I had around.
50a you need #6 wire as I recall
You also need an insulated ground, not a bare ground
Old 06-24-2009, 09:15 PM   #17
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
Things should look like this diagram except you will have a neutral coming from the spa on the load side of the disconnect. that neutral connects to the gfci neutral terminal as shown in the diagram.
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie
Old 06-24-2009, 09:17 PM   #18
Originally Posted by jbfan View Post
Yes. Close to the white wire from the breaker is an opening for the white wire from the hot tub.
You may have to pull the breaker out to see it and wire it in.
Sometime the instructions are really needed!
Some times in life you're not as smart as you think you are! Thank you very much- up and running again.
DaleB is offline   Reply With Quote
Old 06-24-2009, 10:04 PM   #19
Licensed Pro
Golly. It took 17 posts to get to the answer you had in post #2.
Old 06-24-2009, 10:09 PM   #20
I type too slow
Old 06-24-2009, 10:29 PM   #21
UAW SKILLED TRADES
Stubbie's Avatar
My bet is you have the GFCI breaker installed wrong. Wires from the main panel (should be four, hot, hot, neutral, ground)) feed the spa panel. The tub wires (hot, hot, neutral) land on the GFCI breaker. Insulated ground lands on the ground bar. White pigtail from the GFCI breaker lands on the neutral bar.
Yeah I thought the thread was over at that point..... but much to my surprise it continued and I got to post my diagram........... If my diagram had been attached to your post it would have been a sure thread ender
Stubbie
Old 06-25-2009, 04:35 AM   #22
But, then we wouldn't have seen the other problems...
jerryh3 is offline   Reply With Quote
Old 06-25-2009, 06:51 AM   #23
Licensed Pro
Old 06-25-2009, 11:18 AM   #24
That's the best diagram I have seen, very nice
Breaker problem jdhar Electrical 11 06-10-2009 01:18 AM
Sq D Trillaint Breaker problem jmreynol Electrical 3 04-28-2009 07:06 PM
20 Amp Breaker tripping with GFCI panhandlion Electrical 7 12-12-2007 08:59 PM
Outdoor breaker panel questions lhoney2 Electrical 12 07-19-2007 05:44 PM
Breaker Buzz SkipI Electrical 2 07-13-2007 07:48 PM