Bathroom Circuit Question - Electrical - DIY Chatroom Home Improvement Forum
Old 05-16-2013, 04:13 AM   #1
Rewards Points: 197
Question
Hi everyone,
I am wiring our downstairs bathroom basement and had a question. The bathroom will have 2 GFCI's, 1 light switch, 1 Vent Fan.
Can I put all this one 1 circuit. I was thinking of running 12/2 (on 20 AMP Fuse) to the bathroom and then pig tailing and using 14/2 for the lights and switches. 12/2 for the GFCI's and Vent Fan.
cloves is offline   Reply With Quote
Old 05-16-2013, 05:11 AM   #2
Electrical Contractor
kbsparky's Avatar
1) Yes, you can put it all on one 20 Amp circuit
2) NO, you can NOT extend the circuit for lights using #14 wire. You MUST use #12 wire for the lighting if you tap off the 20 Amp GFCI feed.
-KB
The Following User Says Thank You to kbsparky For This Useful Post:
Philly Master (05-16-2013)
Old 05-16-2013, 07:04 AM   #3
Rewards Points: 150
A bathroom requires a 20 amp circuit you are allowewd to power everything in the same bathroom from this circuit but no other rooms. A 20 amp cicuit must be in a minimum of #12 you cannot mix in #14 which is rated for only 15 amps.
usair is offline   Reply With Quote
The Following User Says Thank You to usair For This Useful Post:
MTN REMODEL LLC (05-16-2013)
Old 05-16-2013, 07:49 AM   #4
Super Moderator
joed's Avatar
Rewards Points: 30,950
You need to add your location to your profile. Rules for a bathroom are different in Canada.
Old 05-16-2013, 08:22 AM   #5
Rewards Points: 197
Thanks everyone! Located in North Jersey.
Would it make sense to run this off of the bathroom directly on top, pretty much exact same specs. 12/2 line is currently there?
Old 05-16-2013, 09:26 AM   #6
Electrical Enthusiast
Rewards Points: 504
No, if you plan to wire both lights and receptacles in the bathroom, the bathroom must have it's own dedicated 20 amp circuit. You will be thankful for this when people start plugging in hairdryers and such.
Kyle_in_rure is offline   Reply With Quote
Old 05-16-2013, 10:07 AM   #7
Rewards Points: 3,130
You don't need to use two GFCIs. Use one for the first receptacle in the circuit and the downstream receptacle(s) will also be protected.
Old 05-17-2013, 06:28 AM   #8
Rewards Points: 6,722
Only if the wires are connected to make that so. Many people connect the downstream to the line (either by mistake or because they think it's OK) which of course doesn't accomplish what you're saying.
jeffnc is offline   Reply With Quote
Old 05-17-2013, 08:13 AM   #9
You are certainly correct. That's why I said to install the GFCI as the first receptacle in the circuit. Since the OP is doing the wiring, he should be able to figure out which one that is.
Old 05-17-2013, 06:00 PM   #10
Not sure you understood quite what I meant. I was getting at "Line" vs. "Load". For example, install the GFCI outlet as the first outlet in the circuit.
Add more receptacles "Downstream", connected to the Line output of the GFCI. The downstream receptacles are not GFCI protected.
You have to wire the downstream receptacles to the Load output from the GFCI receptacle for them to be protected. A lot of homeowners get this wrong.
Old 05-17-2013, 07:49 PM   #11
Remodel and New Build GC
MTN REMODEL LLC's Avatar
Rewards Points: 1,162
Yea.... he otta read the directions and wonder about the yellow tape... and be aware of what you told him about.
MTN REMODEL LLC is offline   Reply With Quote
Old 05-17-2013, 08:52 PM   #12
Rewards Points: 512
delete cause i can't read.
Installation is the Reverse of Removal.
The Following User Says Thank You to sirsparksalot For This Useful Post:
MTN REMODEL LLC (05-18-2013)
Old 05-17-2013, 09:18 PM   #13
Rewards Points: 6,652
Originally Posted by cloves View Post
Hi everyone,
Put the lighting & fan on the the current basement lighting circuit, gfci you can feed in most areas off of an existing bath circuit, if you do not have enough panel space, otherwise you would need a new 20 amp circuit if in the U.S. for the bath outlet, Canada can be different in what they require for the max amp for a gfci outlet in baths & kitchens, so always check your code of where you live, since you did not post your location.
Also, if you are updating http://www.diychatroom.com/f18/can-i...12-2-a-178891/ it always helps to reference an old thread in the beginning, if you are continuing asking questions, even though it was all covered in that thread, and yes I am guilty in derailing the last part, because of the fact, that it got into nothing but a huge code cite, and not actually answering the question for the topic at hand.
Question about Plumbing Basement bathroom with PEX dgreen Plumbing 5 03-08-2012 03:28 PM
Kitchen circuit re-design - Existing is a mess darlingm Electrical 5 12-31-2011 09:45 PM
Help! Bathroom Question ryuki Painting 5 02-02-2011 12:17 AM
20 Amp Bathroom Circuit theatretch85 Electrical 3 04-06-2009 09:33 PM
lighting circuit design question amakarevic Electrical 15 10-31-2008 02:11 PM