AFCI Receptacle Without Metal Conduit - Electrical - DIY Chatroom Home Improvement Forum
Old 01-11-2019, 12:11 PM   #1
Rewards Points: 40
Question
AFCI receptacle without metal conduit
Given: There is no requirement for AFCI protection since there is no new work or modifications to circuits.
The electrician was working on the main electrical panel, and recommended adding AFCI protection to the bedroom circuit. Since he did not have a combination breaker for this panel, he installed an AFCI receptacle in the first box (metal) from the panel (metal). The cable between these two is NM, with no conduit.
I later learned that the NEC would have required certain approved metal conduit (or various other options) from the metal panel to the first metal box if this were new work or a circuit modification.
With this AFCI setup lacking conduit, is there: Zero additional benefit; Some partial benefit; or A hazard introduced?
750mV is offline   Reply With Quote
Old 01-11-2019, 12:17 PM   #2
Super Moderator
joed's Avatar
Rewards Points: 404
Re: AFCI receptacle without metal conduit
There is the benefit of the whole circuit being AFCI protected except the short distance to the first receptacle.
I don't see any hazard. It's no different then not having an AFCI.
The Following User Says Thank You to joed For This Useful Post:
750mV (01-11-2019)
Old 01-11-2019, 12:37 PM   #3
Oso954's Avatar
Rewards Points: 2,144
The requirement for conduit between the panel and the AFCI receptacle box is a new work requirement, if you choose not to use an AFCI breaker.
For a circuit modification or extension, the conduit is NOT required.
2017 Code Language:
210.12(D) Branch Circuit Extensions or Modifications Dwelling Units and Dormitory Units. In any of the areas specified in 210.12(A) or (B), where branch-circuit wiring is modified, replaced, or extended, the branch circuit shall be protected by one of the following:
(1) A listed combination-type AFCI located at the origin of the branch circuit.
(2) A listed outlet branch-circuit type AFCI located at the first receptacle outlet of the existing branch circuit.
Exception: AFCI protection shall not be required where the extension of the existing conductors is not more than 1.8 m (6 ft) and does not include any additional outlets or devices.
Oso954 is online now   Reply With Quote
Old 01-11-2019, 12:57 PM   #4
Rewards Points: 40
Thanks for the clarification.
Since the code does not apply in my case, the main question was whether I was getting any additional protection from the new AFCI receptacle, or whether I should try to find a (slim) AFCI breaker for the old GE panel.
Old 01-11-2019, 01:28 PM   #5
Oso954's Avatar
An AFCI breaker for the GE Q-line is going to be the 1 inch, not the 1/2 inch size.
Old 01-11-2019, 01:44 PM   #6
Rewards Points: 40
The GE panel model is: TM2020F mod 1. Circa 1968.
There are one or two free 1" slots, but most are populated with 1/2" breakers.
Tags
ahci , conduit
Cutting Flexiable Metal Conduit Greendfield mobiledynamics Electrical 24 04-18-2015 03:20 PM