Old 05-21-2010, 07:38 PM   #16
Learning by Doing
Leah Frances's Avatar
Thanks - been a long day. Drinking is on the menu for the rest of the ..... weekend.
If I could only remember to THINK about what I was doing before I did it.
Leah Frances is offline   Reply With Quote
Old 05-22-2010, 03:35 AM   #17
" Euro " electrician
frenchelectrican's Avatar
Leah.,
What brand AFCI breaker you have in your load centre I know there are couple brand on early models are little wonky the later one are better.
Merci,Marc
Old 05-23-2010, 07:39 AM   #18
Let's say your AFCI feeds outlets #1 through #10, with #10 being farthest downstream. You know that when all 10 are connected the AFCI trips and when none are connected the AFCI holds.
Disconnect the downstream outlets at #5. If the AFCI holds, the fault is downstream of #6.
If the AFCI still trips, disconnect the AFCI output and connect #6 outlet with a 50' section of Romex to the AFCI output so that the #1 through #5 section is bypassed and disconnected at each end.
By successively halving the sections that are powered or disconnected, and if there is only one fault present, this method should lead you to the fault location.
Old 05-23-2010, 05:53 PM   #19
Learning by Doing
Yes, this is, in fact, the exact type of troubleshooting advice I need.
Old 05-24-2010, 11:06 AM   #20
Forgot step numero uno: first just hook up 50' of undamaged Romex to the AFCI and see that it doesn't trip.
I e-mailed Siemens for info about their arc diagnostic gadget.
50-50 they condescend to answer me.
And. . .Siemens comes through!
The question was referring to the video, and here is their answer.
The lamp is the actu cause of the arc.
for the breaker / tool to trip, there needs to be a draw of over 5 amps on the circuit that is creating an arc.
the breaker is reading the arc but will not trip until there is sufficient current being drawn on that circuit.
the vacuum cleaner draws enough current to trip the device if an arc is present elsewhere.
If the vacuum cleaner were run without the lamp on, there would not have been a trip...
So the AFCI is an AND gate; if
I > 5A
AND
arc
THEN trip.
Which means you can substitute an arcless load that draws more than 5A for the vacuum cleaner while you troubleshoot.
Old 05-24-2010, 11:59 AM   #21
Master Electrician
Rewards Points: 5,080
Siemens AFCI's have built in diagnostics.
brric is online now   Reply With Quote
Old 05-24-2010, 12:43 PM   #22
That tells you it was a GF or an arc that tripped it? Two LEDs, right?
Old 05-24-2010, 08:43 PM   #23
Oui that is correct it have two leds so it will tell you which type of fault.
Merci,Marc
Old 05-24-2010, 08:47 PM   #24
Merci,Marc
La fin du monde est proche
Nah, just kidding. . .
For the GF testing a 50 mA fuse in series with an AC milliammeter may come in handy.
Old 05-24-2010, 09:12 PM   #25
Learning by Doing
Ok. Finally sobering up. My weekends usually last through Monday (DH's day off). I bought some extra AFCI breakers this weekend and I am going to do the following in the AM.
1. Disconnect the ceiling fan
2. Replace tripping breaker with new one
3. See what happens.
THANKS THANKS THANKS for all the help!
Old 05-24-2010, 09:17 PM   #26
Master Electrician
And just what would you do with these?
Old 05-24-2010, 09:22 PM   #27
Yoyizit.,
I will not use that kind of methold of GF testing and the way I do in France we run the megger that will take care of it very fast it is a simple tool once you know to use it in safe manner.
I use it just about everyday in France and in Wisconsin I used it pretty often especally hard to trace fault on AFCI useage.
Merci,Marc
Old 05-25-2010, 07:42 AM   #28
Put them in series with the ground wire, assuming the leakage is being returned through the ground wire.
Old 05-25-2010, 08:07 AM   #29
Master Electrician
Why all the BS? If the current is through the ground wire simply removing it from the buss and touching it to the buss after resetting the breaker will trip the AFCI.
Old 05-25-2010, 09:04 AM   #30
Yes, if the AFCI is not nuisance-tripping. One OP had AFCI trips because he lived near a radio station.
The AFCI is a go/no-go device. Having an LED for arcs and another for GFs is an improvement but when you get misleading results it's time to make measurements with meters.
If those readings also look strange then you need an o'scope.
And I'll check the calibration on my BS filter, sometimes it drifts out of adjustment. . .