Adding A New 220V Outlet To Existing Line - Electrical - DIY Chatroom Home Improvement Forum
Like Tree1Likes
Old 12-31-2016, 08:07 PM   #1
Rewards Points: 14
Adding a new 220V outlet to Existing line
Hi:
I have an existing 220V line run in my garage to a safety switch that is hardwired into my air compressor. I need to add a 220V 6-50R outlet. I would like to do this by adding a new outlet adjacent to an existing junction box, but I'm not sure if this kind of parallel wiring is OK with 220v. I will be turning the air compressor off at the safety switch any time I am using the 220v outlet. Attached is a diagram that I made to try to explain what it is I want to do. If someone more knowledgeable than me could weight in I'd greatly appreciate it!
-Skippy
Skippy77 is offline   Reply With Quote
Old 12-31-2016, 09:22 PM   #2
Rewards Points: 2,564
Re: Adding a new 220V outlet to Existing line
A 50 A socket served by a 30 A breaker - and, presumably, 30 A rated wiring - would not be allowed.
FrodoOne is offline   Reply With Quote
Old 12-31-2016, 09:51 PM   #3
Rewards Points: 14
The device being plugged into this socket is a Miller 211 welder which according to them should be on a 25 or 30 amp fuse/breaker. The welder comes with a 6-50P cord.
-Skippy
Old 12-31-2016, 11:18 PM   #4
-Skippy
The circuit breaker is there to protect the wiring from a load beyond its current carrying capacity. Such a load may cause the wiring to overheat and cause a fire!
If you install a 50 A socket, while YOU may not plug in anything which draws more than 30 A, a subsequent owner may - and it is NOT according to code.
You could rewire and install a 50 A Breaker and a 6-50 socket!
A cheaper option would be, if your device requires no more than 30 A, you could
install a 6-30 socket and
change the cord/plug on the welder.
If this would void the warranty on the welder, you could
make up an adapter with a 6-30 plug and a 6-50 socket.
This also is not "according to code" - but, only you need to know about it!
You also probably need a second 30 A Safety Switch for the new Outlet.
Old 12-31-2016, 11:22 PM   #5
Rewards Points: 14
Thanks for the input FrodoOne. I appreciate it. Is splitting a receptacle off as I proposed acceptable? As long as it is 30 amp.
Old 01-01-2017, 04:08 AM   #6
With the caveat that it should be GFCI protected, I believe so.
However, you should note that I am NOT in North America.
One hopes that someone with better knowledge of the local situation will come to your aid. (Since I have not so far been "corrected" perhaps I have been right, up to this point.)
In this country, virtually ALL circuits must now be protected by RCDs, RCBOs, GFCIs (or whatever name they are given locally) at the main panel or sub panel.
Individual protected outlets were/are available but now are hardly ever used here.
Old 01-01-2017, 10:45 AM   #7
A "Handy Husband"
rjniles's Avatar
Rewards Points: 50
240 volt circuit do not require GFCI under the NEC.
Sent from my RCT6203W46 using Tapatalk
My electrical answers are based on 2014 NEC, you may have local amendments.
The Following 2 Users Say Thank You to rjniles For This Useful Post:
Jim Port (01-01-2017), Speedy Petey (01-01-2017)
Old 01-01-2017, 10:49 AM   #8
A "Handy Husband"
rjniles's Avatar
Rewards Points: 50
Your manufactures instructions call for a 15 or 20 amp circuit with a 25/30 amp fuse/breaker. Don't connect to a 30 amp circuit.
Old 01-01-2017, 12:25 PM   #9
Super Moderator
joed's Avatar
Rewards Points: 29,234
Please explain how this would even be possible.
Old 01-01-2017, 01:07 PM   #10
Rewards Points: 14
I think you're looking at the column for 120V on the right. This welder has an adapter plug that allows it to be powered from either 120v, or 240v single phase. I will be setting it up for the 240v single phase which is the column on the left.
Old 01-01-2017, 01:20 PM   #11
Rewards Points: 28
Agree with that, BUT the only reason NEC hasn't extended itself there is because on instabilities in GFCI logic design -- on the industrial side, that's been largely overcome and GFCIs are available and used at that voltage and higher. I expect NEC to more fully adopt GFCI at higher voltages (for residential) in the near future.
39032637 is offline   Reply With Quote
Old 01-01-2017, 01:22 PM   #12
Rewards Points: 28
OP -- the design you're proposing is a bit messy and with that NEMA 6-50 sitting there future users might be confused (and electrocuted or start a fire). Any decent home inspector or building inspector official would CRINGE.
FrodoOne likes this.
Old 01-01-2017, 01:40 PM   #13
Rewards Points: 14
Thanks for the input. I definitely want to do it the right way. The plug on the welder is a 6-50. I could redo all of this with a 50 amp breaker and appropriately sized wires. It strange that it specifies a 30 amp breaker with minimum 14 gauge wire and has a 6-50P on the welder.
Old 01-01-2017, 02:44 PM   #14
Rewards Points: 28
NEMA 6-50 is the most common on welders (reasonably low duty cycle/input amps varieties) so the Lincolns, Millers of the world use it thinking most shops have 6-50Rs installed.
I have TIG, MIG, SMAW (NEMA 6-50P, L6-20P, L14-30P) and just use short 12" adapters cables, 6-4 SOOW plugged into a NEMA 14-50R...........keeps the "infrastructure" code compliant.......
The 211 is a great MIG Machine...........you can always just change the plug to a 30A type like FrodoOne recommended.............
Is there a magnetic starter on your compressor and are you using time delays in the safety switch?
Old 01-01-2017, 03:08 PM   #15
Rewards Points: 14
The air compressor does not have a magnetic starter. I am using 30 amp time delay fuses in the safety switch. When I installed it I was worried the amps might spike when it kicked on, so far I haven't had any issues with it.
would adding an outlet destroy grandfathering? Toller Electrical 39 09-18-2015 12:19 AM
Help rewiring 220V 3-prong outlet to 4-prong grounded outlet madmaxwell Electrical 7 03-23-2012 07:37 AM
Odd voltages at outlet TJF Electrical 12 11-01-2011 10:13 PM
Converting a 220V two-gang outlet to 110V kevindd992002 Electrical 17 09-30-2011 07:17 AM
Adding outlet to existing circuit. Which way? noone Electrical 10 06-30-2011 10:16 PM