compressor motor shows:
Volts 208-230 continuous.
15 amps
Nap, I like your thinking,....Checked the voltage between the 2 hot wires, = 0, yes, it is off the same phase leg. At the box between the two legs it's 240v.
Now it makes sence to me why it didn't work. I didn't have 240v at the plug.
cruzpilot is offline   Reply With Quote
Old 09-12-2010, 04:38 PM   #17
Originally Posted by a7ecorsair View Post
the black wire and the re-identified white wire (black tape) will go to the two straight terminals and the bare ground will go to the U shape terminal.
At the breaker box, the two wires, black and re-identified white, will go to the two pole breaker and the ground wire to the ground bar.
Corsair, thank you very much. this is what I was looking for.
I basically originally had it connected this way.
At the box, one set of 2 wires, hot and neutral from one of the hangars, and another set from the other. Both went into separate breakers. I thought one was connected to the A and the other to the B side. (I was wrong) they're on the same phase.
One hot from each was connected to the straight terminals, and then I connected the white wires, both connected to the side neutral terminals in the box. I thought I messed up with the neutral wires, which led me to do a google search, which led me to this site.
Old 09-12-2010, 04:44 PM   #18
nap
You talking to me?
nap's Avatar
Rewards Points: 6,290
It is what I do for a living just like several other members that post here. You would be wise to pay attention to what you are being told here. Not only is it for your safety, it is for the safety of others that might end up being involved in your work as well as meeting any applicable codes.
I understood you to have only a 120 volt service. How do you now have 240 volts?
I have 2 hangars, back to back, that have their own 110v supply for the lights and wall outlets.
or did you intend that they each have a 110v circuit for lights and wall outlets? and they come from a panel that is a 120/240 volt service or subpanel?
Old 09-12-2010, 04:46 PM   #19
[quote=frenchelectrican;499724]
You been told in a nice way there are few codes issue allready arise.
Yes, thank you.
One is no receptales below 1/2 meter { 18 Inches }from floor level to that high { Unless stated otherwise with local or states codes }
all recepts are below this, I'm guessing that it was good at time of build. I installed my recept at about 5 feet high to meet with the compressor... is this to high?
Second I did recall that you have a breaker box about 60 meter away { Apx 200 feet } so that part will not meet the circita unless you have electrician to come out and have installed a properly subpanel which it will meet the modern codes.
My mistake, i walk measured it and its only about 30.5 meters.
And I really advise you should get a qualifed electrician to come out and help you with this one.
I will. thank you.
The Following User Says Thank You to cruzpilot For This Useful Post:
frenchelectrican (09-12-2010)
Old 09-12-2010, 05:02 PM   #20
Dave, thanks for changing your pro pic to the USA flag and the WTC towers. I was there that day, the company I worked for last, lost their entire floor staff, and I had a friend miss his flight out of Logan that met with the towers.
Go USA!
Old 09-12-2010, 05:07 PM   #21
no, the hangars have 240 coming in.
Took cover off box, three BIG lines come in, one each side (A, B) and one to ground....I mean neurtal.
I metered across the two hots, A to B and meter read 244v.
[/quote]or did you intend that they each have a 110v circuit for lights and wall outlets? and they come from a panel that is a 120/240 volt service or subpanel?[/quote]
Yes.
Old 09-12-2010, 05:21 PM   #22
Originally Posted by Stubbie View Post
"Ever wonder what happens if you get scared 1/2 to death twice?"
I like these Mensa type of questions. What happens if you get scared 1/2 to death twice in a row? Many answers to this one.
A. As long as you only get scared 1/2 way, you'll never die.
B. mathematically speaking, after being scared twice, you'll still have 1/4 of your life left, then 1/8, 1/16,...you’ll still never die.
C. If after you've been scared, you consider THIS to be your whole life, any and all times "scared 1/2 to death" will only result in half your death momentarily, then you're back to your whole life.
Fun stuff
Old 09-12-2010, 05:30 PM   #23
Local codes can vary
Here a homeowner is allowed to work on his own house - for electric/building, not for plumbing
Any property being rented out or Commercial property must be a Pro
This differs across the country
Now if the hangers were on my property & was not listed as commercial I could run the wire & connect up
While I might be the only person living on my property, it has to be wired to meet code so that anyone else will know what to expect for wiring
And correctly so that no-one will be put in danger
I'm not sure on compressor connections as far as wiring/breaker
Sometimes a larger breaker is required on some motors for startup surge
If that is not required then it seems 12-2 could be used a with a 15a 240v breaker
I could be very wrong on that.....so do not go by my "guess"
Old 09-12-2010, 06:09 PM   #24
" Euro " electrician
frenchelectrican's Avatar
Dave .,
Some of the air compressor motours do have thermal overload switch on the motour that will be not a issue however if sans { without } thermal overload protection this will get little tricky to deal with it.
For example the OP mention 15 amp @ 240 volts { if the motour nameplate is correct } and have thermal protection switch on the motour then yes you can use the larger breaker but there are few restictions you have to follow only if you have hardwired units
If hardwired the NEC code do allowed much larger breaker up to 250% over the rating { before you go any further make sure you read Art 430 and Art 440 first they will mention few restrictions }
Cord and plug set up are not includeing this list { it go out of the window if you try to use Art 430/440 }
Cruz.,
If you have the panel in the hanger and I know you say 30.5 meter away from the load centre now there are two thing to order to meet the codes you will need a local disconnection switch or plug with receptale one of the two will meet the codes depending on which way you wired up the compressour.
By the way NEC code say if over 15.25 meter { 50 Feet } or not in sight of main load centre it must have disconnect switch or plug / recepetale one of the two will work.
The receptale height at 1.524 meter { 5 feet } that is not useally a issue but just make sure you don't block it when you need to unplug for some reason.
Is the Hanger is privite owned or on commercal { rental hanger } ??
If latter per state codes it have be done by electrician but privite owned it kinda toss up BUT let me give you a head up the Hangers are useally classifed as commercal building so you are stuck with commercal codes.
{ This part that where the inspectors will look pretty close on the Hangers }
Merci.
Marc
Old 11-12-2010, 05:11 PM   #25
240V 30amp wiring
thanks
monocle is offline   Reply With Quote
Old 11-12-2010, 05:39 PM   #26
Do it right.
Rewards Points: 77
Originally Posted by monocle View Post
I am replacing my wall oven. The old oven is wired 240V, 30 amp breakers, with 3/10 w/ground NM wire. The new oven is spec'd at 240V 20 amps. Can I use the existing gage wire and just replace the breaker with 20 amp? thanks
you meant 10-3 right? if so then absolutely.
SubSailor is offline   Reply With Quote
Wiring 220V Chandelier for 110V ntxcop Electrical 7 12-26-2012 05:00 PM
Smokehouse Wiring project questions - 220V Beck74 Electrical 5 01-03-2010 11:22 AM
Need help wiring old 220v fan motor HotTommy Electrical 28 02-15-2009 09:15 PM
Wiring a single pole switch into a 220v circuit rlmorgan Electrical 38 10-15-2008 07:59 PM
220V Wiring Mdbuilder Electrical 18 07-10-2008 11:14 PM