I have a water well pump that is 220v, can I come off the well connection with maybe a step down transformer to 110v to run a light in the well house and maybe a light in the shed next to the well house? the well pump pulls 2.5amps, and its on a 30 amp breaker on the outside of the house. not sure if that makes a diff or not. Thanks
dcdoc is offline   Reply With Quote
Old 06-28-2009, 09:05 PM   #2
Electrical Contractor
kbsparky's Avatar
What type of wire runs to the well house? Size of and number of conductor?
If you have the proper cable there, a simple sub-panel should do the trick without the need for a transformer.
Also, where is the pressure switch located?
-KB
Old 06-28-2009, 09:12 PM   #3
2 fingered typer
woodnthings's Avatar
I'd like to see a well pump that pulls 2.5 amps?
That's less than 1/4 HP? Are you sure?
woodnthings is offline   Reply With Quote
Old 06-28-2009, 09:13 PM   #4
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 2,006
If it is like 99.9% of the wells I have seen it is fed with only a 2-wire. If it is newer, or if you are lucky, it will have a ground. A neutral is highly unlikely.
I am also wondering what size wire is feeding this well. WHY is there a 30A breaker if the load is only < 3A?
Old 06-28-2009, 09:35 PM   #5
The pressure switch is located on the front of the tank, very easy to get too. its a brand new set up, about a year old. I'll have to double check the amps for the pump and the wiring tommorow.
Old 06-28-2009, 10:59 PM   #6
The main thing to check is the wiring type and size.
If you have a three wire system that has two hots, a neutral and a ground (wire or conduit), you can probably set a small sub panel and get both 120 and 240 volts out there.
220/221 is offline   Reply With Quote
Old 06-29-2009, 03:16 AM   #7
Even if you only have 2 wires I think you can put in a subpanel and put in a 230v bulb.
http://www.grainger.com/Grainger/items/1E243
Tell me if I'm wrong.
vann is offline   Reply With Quote
Old 06-29-2009, 10:57 AM   #8
J. V.'s Avatar
Rewards Points: 346
Yes, they do make 230 volt bulbs. And yes, a 230 volt bulb requires no neutral. But the motor circuit is a dedicated circuit and I am not certain about a splice for the lamp holder on this circuit. Someone can explain further. I am not sure how this could be done correctly, but yes you are correct, it can be done. But is it compliant? Thats the question. I am asking? Others?
Old 06-29-2009, 11:06 AM   #9
Well putting in a subpanel should take care of the dedicated motor circuit problem, but like you said I'm not sure of the compliance of this to the code.
Old 06-29-2009, 06:51 PM   #10
I like that train of thought. 240V fluorescent strip fixtures should be easy enough to find.
Old 06-30-2009, 12:49 AM   #11
Idiot Emeritus
Rewards Points: 80
A lot of fluorescent fixtures these days have multi-volt ballasts. They will operate on any voltage from 120 to 277. The neutral doesn't need to be grounded.
The older core-and-coils 277 volt ballasts will operate on 240, but the lamps won't last as long, and they won't start as well when it's cold.
There's nothing in the code, that I know of, that says you can't have a 240 volt fixture.
Rob
micromind is offline   Reply With Quote
Old 06-30-2009, 08:54 AM   #12
Rewards Points: 2,350
The only thing I can think of that would prevent a 240 V light in this instance would be the 30 A circuit. In residences (and I would think a pump house counts as part of the residence), 30 A circuits are not allowed to supply light fixtures.
If you changed the breaker to 20 A, or installed a subpanel at the pump, and used a 2-pole switch for the light, you would be good to go. Also, I would put a big label on the light and switch. Something like:
"WARNING: 240 Volts.
Old 06-30-2009, 12:46 PM   #13
Rewards Points: 528
Send a message via AIM to theatretch85
I would think a subpanel in the well house would be fine, but as soon as you have light out there you're going to want outlets for a battery charger or something else in the shed. I would look into the 120 volt route verses the 230/240 volt route, it will be much better in the long run and provide for a lot more flexibility in the future.
theatretch85 is offline   Reply With Quote
Adding 110V outlets to 220V line MarcG Electrical 25 04-29-2009 06:04 AM
Convert 220V to 110V wrldruler Electrical 13 09-15-2008 11:55 AM
110v vs. 220v gunboatbay Electrical 17 05-15-2008 08:09 AM
220v to 2 110v ? Astoldt Electrical 5 12-28-2007 08:16 PM
220v from 110v leboyd Electrical 6 03-19-2006 08:51 PM