I plan to run single conductor #6 to another part of my garage. It will power a small 220 welder and a few other tools. I have enough #6 to supply the two line supplies and enough #8 for the ground.
Will this be OK?
I ask this because I have seen a lot of romex type cable with the ground being a smaller gauge.
What is the ruling and what needs to be considered conserning the size of the ground in a 220 circuit?
Giles is offline   Reply With Quote
Old 01-30-2010, 08:11 PM   #2
Electrical Contractor
jbfan's Avatar
Rewards Points: 960
Does all of the equipment use the same receptacle as the welder.
If you have enough wire, run 3 #6, and a #8, using the third #6 as a neutral, and insatll a 4 circuit subpanel.
You can then run a couple of different size circuit for the equipment.
Yes I am a pirate, two hundred years too late
The cannons don't thunder, there's nothing to plunder
I'm an over-forty victim of fate.
jbfan is online now   Reply With Quote
Old 01-30-2010, 08:22 PM   #3
Idiot Emeritus
Rewards Points: 80
The ground size is based on the breaker size, not the wire.
A #10 ground is good for any circuit up to 60 amps, #8 is 100 amps.
You can go larger, but not smaller.
Rob
micromind is offline   Reply With Quote
2 wire outlets: connect neutral to ground? border collie Electrical 19 04-12-2013 12:29 PM
sub panel ground and neutral daddyrabbit Electrical 3 01-29-2010 06:49 AM
What size wire and what kind of conduit... epeterson777 Electrical 15 02-21-2009 07:43 PM
ground wire in rigid conduit measure thrice Electrical 3 02-03-2009 05:25 AM
ground wire in mc circuit woodturner Electrical 10 08-07-2008 11:34 AM