20A Double Wall Switch For Bathroom - Electrical - DIY Chatroom Home Improvement Forum
Like Tree4Likes
  • 3 Post By rjniles
  • 1 Post By LawnGuyLandSparky
Old 10-16-2019, 10:37 AM   #1
Rewards Points: 688
20A Double wall switch for bathroom
The bathroom was previously wired up having one 14/2 wire going to a single gang, double wall switch. One switch was for general lighting, the second for the vent fan.
While updating this bathroom, I ran a new, dedicated 20 amp circuit for the bathroom vent fan to support a future heater/fan combo unit in the future. I like the current switch setup - single gang box, double wall switch, one switch lighting, and one switch fan. I expected to be able to walk into HD and find a 20A rated double wall switch, but there are none.
HD has two Leviton double switches on their site for order and listed with a 20A rating, commercial grade. I can't imagine this scenario is THAT uncommon to have almost zero selection.
Summary
Bathroom update
Single gang outlet box
Need two switches
1 switch for the 14/2 wire for bathroom lighting
1 switch for the 12/2 wire for dedicated heater/vent fan unit
What's the proper switch to use here? All of the double switches I can find at HD are 15A rated.
dtbingle is offline   Reply With Quote
Old 10-16-2019, 11:06 AM   #2
MarginallyQualified
TarheelTerp's Avatar
Rewards Points: 4,766
Re: 20A Double wall switch for bathroom
You'll need (want) to add a THIRD switch when you add the heat.
For the HEAT... I'd suggest a timer of some sort and a different extra j-box.
The current switch's and set up is fine for the light and fan.
Old 10-16-2019, 11:50 AM   #3
Rewards Points: 688
Adding the third switch or a separate box if a heater/vent combo is put in makes sense.
But how do you get around the issue of 20 amp breaker, 12/2 dedicated wire for current vent only fan, in a single gang box with a double wall switch?
I suppose I could swap the 20 amp breaker with a 15 amp breaker and just use normal 15A rated double wall switch. Then if it's ever upgrade to a heater/fan combo, the 20A breaker could be put back in and install another outlet box for heat/fan functions.
Old 10-16-2019, 12:01 PM   #4
Oso954's Avatar
Rewards Points: 2,138
Go to an electrical supply house, not a big box. They should have what you are looking for.
Or look on Amazon. Here is an example.
https://www.amazon.com/Leviton-5334-.../dp/B0033PSGC8
Oso954 is offline   Reply With Quote
Old 10-16-2019, 01:06 PM   #5
A "Handy Husband"
rjniles's Avatar
Rewards Points: 984
You don't need a 20 amp switch. You can use a 15 amp switch on a 20 amp circuit.
Sent from my Moto E (4) Plus using Tapatalk
jbfan, mpoulton and brric like this.
My electrical answers are based on 2017 NEC, you may have local amendments.
rjniles is offline   Reply With Quote
Old 10-17-2019, 01:45 PM   #6
Rewards Points: 688
This is what I was suspecting. NEC 210.21(B)(3) discusses how you can use 15A receptacles on 20A circuits. Had trouble finding where it discusses 15A switches on 20A circuits.
From various forum posts, my understanding is that the switch is sized for its load. For example, in my case, it's a 20A breaker with 12g wire to supply power for bathroom vent fan. This bathroom vent fan specifies 14g or larger wire. This means my switch only needs to be rated for 15A since the load only requires this - EVEN though 12g wire is used from breaker to switch and from switch to vent fan.
Even if the bathroom vent fan was upgraded to a bigger heater/vent/light combo unit that calls for a dedicated 12g/20A circuit, the 15A switches would still suffice because most of the double/triple wall switches are rated for 20A total, 15A each switch. So the 1400/1500W heater runs to one switch, exhaust fan to another switch, and the light to the third switch - all falling within the 15A limit per switch.
Does this sound correct?
Old 10-17-2019, 01:55 PM   #7
Rewards Points: 680
That's exactly correct.
LawnGuyLandSparky is offline   Reply With Quote
The Following User Says Thank You to LawnGuyLandSparky For This Useful Post:
dtbingle (10-17-2019)
Old 10-17-2019, 05:44 PM   #8
retired framer
Rewards Points: 17,524
I found this, if some one want to check it.
Article 404.14(F) Cord- and Plug-Connected Loads.
Where a snap switch or control device is used to control cord- and plug-connected equipment on a general-purpose branch circuit, each snap switch or control device controlling receptacle outlets or cord connectors that are supplied by permanently connected cord pendants shall be rated at not less than the rating of the maximum permitted ampere rating or setting of the overcurrent device protecting the receptacles or cord connectors, as provided in 210.21(B).
Do not use flat bottom gables with scissor trusses.
https://www.fema.gov/media-library-d...6/chapter7.pdf
figure 7-14
Old 10-17-2019, 06:03 PM   #9
retired framer
Here is a 3 function 20 amp switch by Broan - nutone.
https://www.homedepot.com/p/Broan-Nu...-66V/202919959
figure 7-14
Old 10-17-2019, 09:43 PM   #10
Rewards Points: 680
A bathroom HVL is not a cord and plug connected load.
mpoulton likes this.
Old 10-17-2019, 09:53 PM   #11
retired framer
I read more about that switch and it does say 15, 15 and 5 amps,
figure 7-14
Old 10-18-2019, 12:58 AM   #12
Rewards Points: 330
Came with house.
If you find out more about these please post. I would like a new cover.
slipparee is offline   Reply With Quote
Old 10-18-2019, 04:26 AM   #13
MarginallyQualified
Not a problem. Here's a link to some
Old 10-18-2019, 07:04 AM   #14
Super Moderator
joed's Avatar
Rewards Points: 406
Came with house.
They are known as Despard switches.