20a To 15a Adapter For Treadmill? - Electrical - DIY Chatroom Home Improvement Forum
Old 05-15-2010, 12:32 PM   #1
20a to 15a adapter for treadmill?
I bought a commercial treadmill that requires a 20a outlet because of the right angle prongs. I only have a 15a breaker. I can't tell what guage the wire is. So I don't know if I should replace the breaker with a 20a one and replace the outlet. or there is an adapter that converts it for sale. The owners manual says not to use an adapter because it needs to be properly grounded to prevent electrical shock. I don't understand because I thought the only grounding prong was the big fat round one. Any comments? Thanks
shockwave is offline   Reply With Quote
Old 05-15-2010, 12:42 PM   #2
The device needs a 20a circuit
So you need to put it on a 20a circuit
Do not install a 20a breaker without verifying that ALL wiring is 12g
Old 05-15-2010, 12:43 PM   #3
Rewards Points: 2,800
If you can make or buy a 20 amp 3 hole receptacle to 15 amp 3 prong plug adapter then it would still be properly grounded. You would have to leave the 15 amp. breaker in place down at the panel if the circuit has 14 gauge wire.
Is there any sticker or nameplate on the treadmill stating how many amps it needs?
The treadmill may or may not draw more than 15 amps and if it does then it will trip a 15 amp breaker.
Stick to your lawn watering schedule until it really starts to pour. After the storm you have only the same number of rest days you always had and then you need to start watering again.
Old 05-15-2010, 12:49 PM   #4
Rewards Points: 306
Go here http://www.voltec-industries.com/nema_chart.html and pick the plug you have. Post the NEMA number for that plug. If the treadmill lists the machine for a 20 amp circuit, that's what you will need. You cannot put a 20 amp breaker on #14 wire. It must be #12. While not compliant, if the treadmill current (amps) does not exceed the 15 amp circuits capacity, I would just change the receptacle to match the plug and mark the receptacle as being 15 amp only!
Where are you located?
Old 05-15-2010, 01:03 PM   #5
None of the wiring is labeled. How can I verify the wiring is 12ga?
Old 05-15-2010, 01:07 PM   #6
The plug is 5-20p. The treadmill is rated for 13a. Washington State
Old 05-15-2010, 03:54 PM   #7
I just found out that the wiring is 10gauge. Its on a 15a breaker. There are 2 outlets on that breaker
Old 05-15-2010, 04:01 PM   #8
Sparkaholic
Rewards Points: 150
Send a message via Yahoo to sparks1up
If the circuit wire and its respective neutral are both #12 or larger (#10 is larger than #12) you can replace the breaker with a 20-amp breaker and the receptacle with a 20-amp receptacle.
#10 sounds pretty big to have a 15-amp receptacle connected to it...are you sure it is #10?
Answers based on the mood I am in when you ask!
sparks1up is offline   Reply With Quote
Old 05-15-2010, 04:24 PM   #9
Licensed electrician
Rewards Points: 3,646
Very strange that someone installed wire so large for a 15 amp circuit.
Old 05-15-2010, 04:41 PM   #10
The wire says romex 10/3. Its in the garage, maybe they installed it that for tools?
Old 05-15-2010, 05:07 PM   #11
Idiot Emeritus
Rewards Points: 80
If the wire is indeed 10/3, it'd be ok to change the breaker to 20 amp. All parts of the circuit must be #12 or larger, it sounds like they are.
I would then get a 20 amp receptacle, it looks just like a 15 amp one, except when looking at it with the ground down, the slot on the left will be a T shape. 20 amp, 125 volt. NEMA 5-20. Don't get the 20 amp 250 volt one. It's the same, except the right slot is T shaped. You can get a single or a duplex, your choice. Around here, the big-box stores have them.
With this, no adapter is needed.
Rob
micromind is offline   Reply With Quote
The Following User Says Thank You to micromind For This Useful Post:
shockwave (05-15-2010)
Old 05-17-2010, 08:28 AM   #12
Just call me Andrew
Rewards Points: 1,032
Are you sure all the wiring on this circuit is #10? I would imagine that most of the wiring is hidden in the walls, and there may be other outlets and lights on this circuit as well.
Andrew
secutanudu is offline   Reply With Quote
Old 05-17-2010, 12:49 PM   #13
Rewards Points: 306
If it starts in the panel as #10 and is #10 at the receptacle, its number 10 as far as I am concerned.
OP. You lucked out this. You do know that? That circuit could be 30 amp if you needed it.
Tags
15a to 20a , adapter , treadmill
Modifying laptop ac adapter - Confused. miller108 Electrical 7 01-14-2013 08:49 AM
Vacuum Adapter for Dewalt D26441 llckll Tools 5 02-12-2010 08:21 PM
Trap Adapter Leak? kcrossley2 Plumbing 6 01-27-2010 12:55 AM
Pitless Adapter Submersible Pump Wild Blue Plumbing 5 08-31-2009 01:02 PM
Removing 2" marble toilet flange adapter for handicapped proofer Plumbing 20 04-21-2008 04:31 PM