Old 03-28-2010, 05:09 PM   #16
JackDuich's Avatar
I don't have a large RV but the workshop I'm building can hold one - I think they have 50amp 110V feeds, which is a ridiculous way of using power, but it is what it is. I know they have 30amp 110 feeds. So, I guess it would be a possible 50 amp load on the neutral. If I have to use 3/0 for the subpanel hots I'd use a 2/0 for the neutral.
I've been told to run at least a #6 for the ground down the conduit with the 2 hots & neutral. Can do. I also believe 1 8' copper ground rod at the sub-panel will suffice. Thought I'd use the same AWG as the neutral to connect the ground rod to the panel ground. That may be overkill since my house feed to 2 200 amp panels is 2 runs of 3/0 with 2/0 neutrals. A single ground rod is near this pair of panels with a 1/0 or 2/0 tied to it.
Thanks for your help - can to comment on my wire size thinking? I was going to use 2/0 hots but was told the sub-panel has to be a size larger than the feeds to the main panel(s). Neutral typicaly 1 size smaller..
JackDuich is offline   Reply With Quote
Old 03-28-2010, 06:24 PM   #17
Master Electrician
Rewards Points: 5,084
Siemens ECLK225 sub-feed lugs.
brric is online now   Reply With Quote
Old 03-29-2010, 01:51 AM   #18
Electrical Contractor
kbsparky's Avatar
Originally Posted by JackDuich View Post
I.... I think they have 50amp 110V feeds, which is a ridiculous way of using power, but it is what it is. I know they have 30amp 110 feeds. So, I guess it would be a possible 50 amp load on the neutral. If I have to use 3/0 for the subpanel hots I'd use a 2/0 for the neutral....
Larger RVs have a 50 Amp 240 Volt feed, using a standard range cord configuration NEMA 14-50.
Using a 2/0 for your panel feeder neutral will be sufficient in any case.
...I've been told to run at least a #6 for the ground down the conduit with the 2 hots & neutral. Can do. I also believe 1 8' copper ground rod at the sub-panel will suffice. Thought I'd use the same AWG as the neutral to connect the ground rod to the panel ground. That may be overkill since my house feed to 2 200 amp panels is 2 runs of 3/0 with 2/0 neutrals. A single ground rod is near this pair of panels with a 1/0 or 2/0 tied to it....
A ground rod is only capable of dissipating a limited amount of juice. Using anything larger than a #6 is a complete waste of resources, since the ground rod can't handle any more. This has been tested and confirmed by independent labs, and the Code recognizes this limitation.
-KB
Multiple Panel Question theatretch85 Electrical 7 09-29-2016 07:15 PM
GFCI Needed on Sub Panel Feed from Underground? beaker353 Electrical 1 01-13-2010 09:23 PM
Replacing 2 Sub Panels with 1 Larger Panel GuitarJack Electrical 7 08-25-2009 08:43 PM
Feed Sub Panel From Sub Panel jamiedolan Electrical 3 02-03-2009 12:22 PM
Replacement Meter Panel leonard_voet Electrical 19 04-09-2008 10:27 AM