#14 pig tails ok with 20 amp recept circuit?
20 amp breaker protecting the circuit, with #12 romex to multiple
receptacle, using 15 amp recepticles. All ok so far.
How about the pigtails on the receptacle in the outlet boxes - can they be #14 or must they be #12 as well?
If must be #12, why - as each receptacle is rated for 15 amps?
Old 12-13-2009, 10:09 AM   #2
The circuit is rated at 20a so #12 must be used
Each plug is rated at 15a, 20a pass thru on the device
Old 12-13-2009, 10:21 AM   #3
Each recept is pigtailed - so it's electrically an extension of the recept connection - 20 amp would not pass through the device/pigtail. No?
Old 12-13-2009, 10:27 AM   #4
If one plug is pulling 12a - vac cleaner
and other devices in a power strip are pulling 8a
That would max out the circuit pulling 20a....thru 14g wire
Not allowed by code...not safe
Old 12-13-2009, 11:11 AM   #5
Got it now - two devices on the same recept. could exceed.
thx!
Vince
Old 12-13-2009, 11:22 AM   #6
Yes, it would not happen that often -at least for me, but some people use 1500w space heaters & high draw items
And they only worry about the load on a circuit if the breaker kicks off
Old 12-13-2009, 11:34 AM   #7
The screw connections on the outlets are rated at 20 amps.
Billy_Bob is offline   Reply With Quote
Tripping breakers,neutrals,120 volts and 240 volts OH My!!! Stubbie Electrical 17 06-11-2011 06:09 AM
Circuit advice for finishing basement Straightgrain Electrical 16 03-25-2009 09:07 AM
Wiring a single pole switch into a 220v circuit rlmorgan Electrical 38 10-15-2008 07:59 PM
So lost - electrical requirements please help lapsis9 HVAC 4 12-20-2006 08:09 PM