Hi, I have a double ganged light switch+receptacle box on my kitchen counter wall. The light switch is on a 15A living room circuit and controls an overhead kitchen sink light, not GFCI protected. The receptacle is on a 20A kitchen circuit and is GFCI protected. I don't like this setup, because 1) I almost forgot to switch off the living room circuit breaker while working in the box; 2) I'd prefer having the light switch be protected by the GFCI circuit as well since it's close to the sink. I'd like to feed the light through the 20A GFCI circuit instead, and cap off the 15A/14AWG wires. The receptacle is the last one on the GFCI protected 20A/12AWG circuit, is it ok to add the switched light to this last receptacle through the existing 14/2 romex for the light?
What does the current U.S. NEC code say about my situation? thanks
Attached drawing describes the situation.
12 AWG circuit, 14 AWG cable for the last load -- a switched light-wiringquestion.jpg
ElectricIQ is offline   Reply With Quote
Old 04-12-2019, 06:19 PM   #2
Rewards Points: 1,234
Re: 12 AWG circuit, 14 AWG cable for the last load -- a switched light
No. Cable ampacity must be equal or greater than the branch breaker.
mpoulton likes this.
curiousB is offline   Reply With Quote
Old 04-12-2019, 06:35 PM   #3
Rewards Points: 80
OK, thanks. Are switches on kitchen counter walls required to be GFCI protected?
Old 04-12-2019, 06:35 PM   #4
Property Mgt/Maint
Rewards Points: 6,230
Maybe separate the double box into separate single boxes.
Tom153 likes this.
[political signature removed]
Yodaman is offline   Reply With Quote
Old 04-12-2019, 06:44 PM   #5
Super Moderator
joed's Avatar
Rewards Points: 22,634
No they are not.
Can't do that. Kitchen counter receptacle can't have lights on the circuit by code.
Arrange the two breakers so they are beside each other and install a handle tie so they both go off together.
Old 04-12-2019, 06:46 PM   #6
Rewards Points: 80
Thank you for the definitive answers. I will just leave it be then.
Old 04-13-2019, 07:19 AM   #7
So does that mean all the commercial buildings with 14 gauge, 3 wire whips to the lay in fixtures on 20 amp breakers are wrong.
Tom153 likes this.
7635tools is online now   Reply With Quote
Old 04-13-2019, 08:03 AM   #8
A "Handy Husband"
rjniles's Avatar
Rewards Points: 378
As long as the whip was manufactured as part of the fixture it is complaint. It is a listed assembly, no different that a light fixture using 16 gauge wires that connect to a 15 or 20 amp circuit.
My electrical answers are based on 2014 NEC, you may have local amendments.
rjniles is offline   Reply With Quote
Old 04-13-2019, 09:07 AM   #9
So all the fixture whips that are bought or made with 14 gauge wire are wrong if they weren’t supplied with the fixture?
Old 04-13-2019, 09:48 AM   #10
A "Handy Husband"
rjniles's Avatar
Rewards Points: 378
Correct, they are not tested as a listed assembly. They can be used on a 15 amp circuit.
Sent from my Moto E (4) Plus using Tapatalk
Old 04-13-2019, 01:17 PM   #11
Rewards Points: 592
Yes. The way it's wired is exactly the way it's supposed to be wired. Just be careful when working on electricity, and be sure test ALL wires in a box for power before working on anything in that box.
BluegrassGuy is offline   Reply With Quote
Old 04-13-2019, 01:55 PM   #12
Deleted Member
Shadow99's Avatar
Rewards Points: 858
There are tap rules for lighting. So you can run a smaller conductor from a junction box to the fixture, even if it isn't part of the listed fixture.
You can't do it from the switch thou.
Shadow99 is offline   Reply With Quote
Old 04-13-2019, 03:58 PM   #13
A "Handy Husband"
rjniles's Avatar
Rewards Points: 378
Tap rules are beyond the scope of most DIYers experience and are very easy to misunderstand and misuse. The OPs situation is not within the scope of an allowable tap.
Old 04-15-2019, 08:10 AM   #14
Rewards Points: 1,321
Sounds to me the issue isn't the boxes, it's his brain forgetting that the light and outlet are on separate circuits. Unless you mean to further separate the switch and outlet in some fashion to distinguish one from the other, like actually moving the separate boxes a few inches apart.
huesmann is offline   Reply With Quote
Old 04-15-2019, 12:28 PM   #15
Rewards Points: 978
Just use a Sharpie and write a note on the yolks of the switch/receptacle, or on the back side of the cover plate that says "2 circuits in this box!" Or label them as "Ckt 1" and "Ckt 2" or whatever
RAL238 is online now   Reply With Quote
Wiring an added recessed light circuit with 1 dimmer and one switch Username10 Electrical 27 03-12-2019 12:10 AM
Routing 2 electrical 14/2 cables in a bookshelf Kcrew98 Electrical 2 03-11-2019 11:16 PM
Connecting a cable light system to a track light system megabyzus Electrical 42 11-17-2013 07:06 PM
Adding additional light fixture to switched circuit woodardhsd Electrical 5 07-07-2011 09:06 PM
new light to existing switched light sirsparksalot Electrical 4 04-22-2011 03:23 PM