100 amp service conduit size
My city is on NEC 2008.
I just had a 60amp panel replaced with a 100 amp breakers.
The electrician did not replace the 1" conduit.
He claims this is allowed by NEC.
If memory servs me correct he used #2 aluminum.
I thought 100 amp SEC required 1-1/4 conduit minimum.
Who is correct here?
michaelcherr is offline   Reply With Quote
Old 11-10-2010, 04:52 PM   #2
So you have (3) #2 alum going thru 1" conduit ?
PVC conduit or ?
Fill calc I found seems to indicate that 1" is the min allowed
But not 100% sure
Old 11-10-2010, 04:57 PM   #3
Rewards Points: 330
at least 1 1/4,but 1 1/2 better.over fill with 1"
oleguy74 is offline   Reply With Quote
Old 11-10-2010, 06:08 PM   #4
Electrical Contractor
kbsparky's Avatar
According to table C.10 in chapter 9 of the Code, one can install up to (3) #2 type XHHW conductors in a 1" PVC schedule 40 conduit.
Same allowable for installation in a 1" rigid metal conduit (table C.8(A).
However, table C.9(A) for schedule 80 PVC only allows two such conductors.
DO you know which type of conduit was used here?
-KB
Old 11-10-2010, 06:23 PM   #5
Rewards Points: 330
yep...read for #1xhhw.
Old 11-10-2010, 10:16 PM   #6
Rewards Points: 256
It's a metal conduit.
Lennox service valve questions leeh1212 HVAC 12 07-26-2013 08:59 AM
is UG conduit size change legal? krazni Electrical 1 07-13-2010 02:17 PM
Underground 240v single phase residential supply DIYALLTHETIME Electrical 11 03-05-2009 09:25 AM
how determine size of service tikicarver Electrical 2 01-29-2008 08:10 PM
Service size pipe 3/4 or 1 inch? kgphoto Plumbing 6 01-29-2008 06:23 PM