No power to Inducer
He guys/gals,
My heater stopped working a week ago. Its a 2008 honeywell system.
AC works fine.
Main blower come on with heat request. heat sequence never starts.
Pressure switch is fine.
But the inducer never starts.
I powered the inducer straight to a 120v plug and it runs fine, no bearing or jamming issues.
I am not getting power from the mother board to the inducer. The rest of the board has power. I checked the terminals on board for the inducer and have good continuity but I am not getting power. I pulled the board off and checked the back for solder joints. Everything 'looks' good. no breaks or burn marks etc.
After everything i have read and tested, i am at the conclusion it has to be the mother board (maybe one of the relays or something)
Does that sound right? Any help would be greatly appreciated.
eball is offline   Reply With Quote
Old 04-20-2016, 02:19 PM   #2
Hvac Pro
yuri's Avatar
Rewards Points: 1,536
Re: No power to Inducer
As long as you have 24 volts from W to C at the board the inducer should start. The relay for it may be shot. Try gently tapping on the black plastic relays. Still would need a new board as tapping won't fix it.
Old 04-20-2016, 02:49 PM   #3
Rewards Points: 604
Check the high limit switch - if it's stuck open any modern furnace will behave as yours is, not sure if a call for heat is needed or not.
Check for error codes.
If all the safeties are fine, the connections are fine and the board is not applying power to the inducer with a call for heat, yes the board is bad.
I am not in the business of any trade I give advice on. I have non-professional hvac experience + good knowledge of theory. Attempt repairs at your own risk. Never jump out safeties - especially pressure switches - on a furnace for testing with fuel supply on; use a meter. Do not troubleshoot with live line voltage present unless there's no alternative.
user_12345a is offline   Reply With Quote
Old 04-20-2016, 02:58 PM   #4
Rewards Points: 14
No volts at W/C.
I am getting 24V straight off transformer.
Old 04-20-2016, 03:02 PM   #5
Rewards Points: 14
Originally Posted by user_12345a View Post
Check the high limit switch ....
No error codes.
Not sure how to check high limit switch?
Old 04-20-2016, 03:16 PM   #6
Rewards Points: 14
Ok, just checked limit switch. Read 0V between terminals.
Old 04-20-2016, 04:25 PM   #7
Rewards Points: 907
If you have 0 volts on W/C when the stat is calling for heat, then you have a stat or wiring problem.
Also check R/C.
Bitters is offline   Reply With Quote
Old 04-20-2016, 04:43 PM   #8
Rewards Points: 14
Also check R/C.
i have 24V on R/C and G/C.
nothing on W/C or Y/C.
Old 04-20-2016, 04:59 PM   #9
Rewards Points: 3,230
You should have 24 v between Y/C and W/C when the cooling or heating is calling only. Or else those things will not run.
roughneck is online now   Reply With Quote
Old 04-20-2016, 05:07 PM   #10
Rewards Points: 14
Thumbs up
Also check R/C.
AHA!!!
We recently switched our thermostat. The W wire had slipped out!!!
Didn't occur to me since everything else was working.
Thanks boys for the help!
The Following User Says Thank You to eball For This Useful Post:
Bitters (04-20-2016)
Old 04-20-2016, 05:11 PM   #11
Hvac Pro
yuri's Avatar
Glad you got it fixed.
We always start with the obvious before replacing expensive boards.
Tags
hvac , inducer , inducer won't run , mother board
Power problems on second floor, first floor is fine rarken1 Electrical 21 05-16-2015 12:42 PM
Inducer not getting power olympiadis HVAC 11 02-02-2015 02:08 AM
Dishwasher Power Supply Captain.Sassy Electrical 14 09-14-2011 06:28 AM
Bryant Plus 90 398AAZ inducer motor PCWilson HVAC 10 02-27-2011 05:55 PM
Dumb electrical question about potentially overloading a power socket zapp Electrical 2 02-18-2011 10:43 AM