Old 02-23-2020, 11:50 AM   #16
Rewards Points: 30
Re: HRV wiring
Thank you so much.
I might be back for more guidance once I receive the part.
surferdude2 likes this.
Pauly1971 is offline   Reply With Quote
Old 02-23-2020, 03:24 PM   #17
surferdude2's Avatar
Rewards Points: 666
Re: HRV wiring
You'll be welcome back and also expected back to report your success so others may possibly benefit later when reading this thread.
As I stated, I can't be sure of the quality of those current detector switches you linked since the only ones I ever used were much more expensive. We used them to protect expensive 3-phase equipment from getting damaged due to single phasing when one phase goes off, so a couple hundred dollar item was justified. In your situation, if they fail, it won't cause any damage so not to worry.
Pauly1971 likes this.
surferdude2 is online now   Reply With Quote
The Following User Says Thank You to surferdude2 For This Useful Post:
Pauly1971 (02-26-2020)
Old 02-26-2020, 05:14 AM   #18
Rewards Points: 30
Re: HRV wiring
I'm back.
I received the switch. Do I have to calibrate it?
Old 02-26-2020, 09:37 AM   #19
Rewards Points: 666
Re: HRV wiring
Yes, once you get it installed, you need to set it properly.
Start with the adjustment potentiometer set at the highest position (fully clockwise).
Turn the HRV system on to the high setting.
Rotate the current switch potentiometer counterclockwise slowly until the blower starts up and then a little bit more. It's not critical... estimate how much rotation counterclockwise is left and setting it onward to 1/4 of that amount should be OK.
Then set the HRV to the medium setting and verify that furnace blower stops.
That should do it.
Pauly1971 (03-01-2020)
Old 02-29-2020, 03:31 PM   #20
Rewards Points: 30
Re: HRV wiring
I went for it today.
As per your instruction I turned the screw clockwise but it just spins to no end. I do hear a clicking sound. The red nor the green lights don't light up.
Bad switch?
Old 02-29-2020, 03:57 PM   #21
Rewards Points: 666
Re: HRV wiring
If you have it wired right, then it may be a defective switch. If you have that Orange wire running through the hole on the switch and the switch connections in series with the fan control wire, it should be working unless there is a problem elsewhere in the furnace control circuitry.
For a test, remove one of the wires on the current sensor switch and see if the fan stops. If it does, the switch is not working.
If the fan doesn't stop when tested as above, there is a problem elsewhere and the switch isn't connected properly to the furnace to control the fan as needed.
Be sure the thermostat is not set to keep the fan on all the time.
Old 03-01-2020, 12:35 PM   #22
Rewards Points: 30
Re: HRV wiring
Today I was able to read and follow instructions. haha
I connected it according to your instructions. The green light on the switch is lit when I select max on the HRV but the furnace fan does not turn on.
When the furnace calls for heat, the red light on the switch is lit.
Old 03-01-2020, 12:58 PM   #23
Rewards Points: 666
Re: HRV wiring
It's counter intuitive since the green light means the switch is off and the red light means it's on.
With the HRV running in the high mode, adjust the sensitivity control of the switch until the red light comes on. That should cause the furnace blower to start running.
Old 03-01-2020, 02:01 PM   #24
Rewards Points: 30
Re: HRV wiring
It works like a charm. Awesome!
Surferdude2 your knowledge base is incredible. I appreciate greatly the time you took to help me out.
Cheers