I have a Bard oil furnace and Goodman 2.5 ton a/c and the fan relay gets hot, too hot to touch. I have replaced the entire fan center as one of the terminals burnt. I have checked the blower motor and it is pulling 12 amps. The fan center is a 120/24v,40va relay so 12 amps should be fine. It gets shot in both heat and a/c mode.
elishaman is offline   Reply With Quote
Old 08-09-2020, 12:00 PM   #2
Rewards Points: 918
Re: fan relay getting hot
12 amps seems pretty high. What is the amp rating of the motor?
57TinkerMan is offline   Reply With Quote
Old 08-09-2020, 12:09 PM   #3
Hvac Pro
yuri's Avatar
Rewards Points: 246
Check the 24 volts from the transformer.
If the relay is getting low voltage on G then the internal coil may get hot.
You should get 24 volts from G to C when the AC is on.
12 amps on a motor sounds high also but that won't heat the relay up.
Check the voltage to the furnace also. You should be getting between 110-120 volts. If it is low then the 24 volt transformer side will be low also.
Old 08-09-2020, 12:28 PM   #4
Rewards Points: 918
24V Coil not in play in heat mode?
Old 08-09-2020, 12:48 PM   #5
Hvac Pro
yuri's Avatar
Rewards Points: 246
It is a oil furnace and if the temp sensor for the heating is in the 24 volt circuit it could be.
I would have to see the wiring diagram.
Most newer furnaces don't use the old school 120 volt bi-metal controls.
It could have a normally open and closed circuit interlocked for heating and cooling.
Old 08-09-2020, 12:57 PM   #6
Rewards Points: 2
I am getting 25.3 vac from G to C with a/c running
Old 08-09-2020, 12:58 PM   #7
Rewards Points: 2
The blower motor is drawing 6.9 amps.
Old 08-09-2020, 01:01 PM   #8
Rewards Points: 2
118 volts ac at the fan center connections
Old 08-09-2020, 01:06 PM   #9
Rewards Points: 2
It gets hot in both heat and cool modes
Old 08-09-2020, 01:07 PM   #10
Rewards Points: 2
wiring schematic is in above post
Old 08-09-2020, 03:00 PM   #11
Rewards Points: 338
Hi, what is the FLA of the motor, check the motor name plate, does that motor spin freely?
Geo
Geochurchi is online now   Reply With Quote
Old 08-09-2020, 04:01 PM   #12
Rewards Points: 2
Can not gain access to the plate on motor. Yes it does spin free
Old 08-10-2020, 12:56 PM   #13
surferdude2's Avatar
Rewards Points: 944
I'd test the capacitor on that motor just for laughs. That's a bit too much current for what is probably a 1/3 hp motor.
It's a bit of a stretch to blame that for the contactor coil heating up but stranger things have happened. I suspect the entire contactor may be heating up beyond normal spec.... the contacts may have developed an abnormally high resistance. You may have both of those problems to deal with... fortunately they're both cheap parts and easy to get.
Ah, but I was so much older then...I'm younger than that now
surferdude2 is offline   Reply With Quote
Old 08-10-2020, 02:22 PM   #14
Rewards Points: 2
It ie a 1/3 ,hp motor. Rated at 6.7 amps
Old 08-11-2020, 09:14 AM   #15
Rewards Points: 944
Close enough in that case. I'd now replace the contactor and expect that would be the fix or at least get one on hand since you have been warned.