Condenser Unit Troubleshoot - HVAC - DIY Chatroom Home Improvement Forum
Old 09-07-2020, 05:10 PM   #1
Rewards Points: 42
Condenser unit in an 8 year old split system is getting adequate voltage on the load side of the contactor, but won't start. Seems to want to (i.e., it makes a buzzing/hissing sound before I shut it off). Fan doesn't spin either.
What is the suggested diagnostic path from here? I'd like to rule out any simple-to-identify causes before I call in help.
Checking the capacitor is next?
Thanks.
Riddler is offline   Reply With Quote
Old 09-07-2020, 05:26 PM   #2
Rewards Points: 716
Re: Condenser Unit Troubleshoot
Is this a heat pump or straight air conditioner?
Is it getting control voltage? Contactor pulling in? Power on both poles?
roughneck is online now   Reply With Quote
Old 09-07-2020, 05:45 PM   #3
Rewards Points: 42
Straight A/C
Control voltage is fine. Contactor is working to deliver full voltage on the load side.
Attached (hopefully) is a pic of the capacitor. Because the condensor hums and the fan doesn't turn, maybe toubleshoot the cap next? The cap has three wires. The yellow comes from the load side of contactor. The blue and brown go into the condenser housing, probably to the motor, correct?
Discharge the cap and then test it with a VOM?
Old 09-07-2020, 06:04 PM   #4
Rewards Points: 716
Yes, test the capacitor.
Old 09-08-2020, 10:34 AM   #5
Rewards Points: 344
Test your Cap with a MF meter, not VOM.
clocert is offline   Reply With Quote
Old 09-08-2020, 11:13 AM   #6
Rewards Points: 716
A lot of general use meters have a capacitance function. No need for a specific one use only device.
But the OP will need a meter capable of reading capacitance.
Old 09-08-2020, 12:05 PM   #7
Rewards Points: 42
Well, my meter only measures ohms, not MFD.
I set my DMM to the highest ohm setting (2000K).
On the Herm and C terminals, the reading rose from 0 to 1220, and stopped. Not sure why it didn't discharge and return to 0 for another climb.
On the Fan and C terminals, reading didn't move. Stayed at 0.
The cap ratings by the way are 40 MFD compressor side and 5 MFD fan side.
Anyway, weird enough that I'll go ahead and invest $35 to get a replacement by 2-day courier.
Old 09-08-2020, 12:22 PM   #8
Rewards Points: 42
If the new cap doesn't cure things, what next.
As I said, when the contactor juices things, there is a clunk followed by a buzz/hum. Neither compressor or fan runs though. Same thing every time I flip the disconnect to "on."
The applicable wiring diagram (attached) seems to show a separate start cap and relay (or thermistor) as included on some units, but I don't see any on mine. Can a 2 1/2 ton condensor unit only have a dual run cap? How do they get the compressor started? It's frustrating that the only parts and wiring diagrams I can find don't tell me exactly how my particular model/unit is set up. The manufacturer (Day/Night) only bothers to make generalized diagrams that are supposed to apply to a group of models/units.
Old 09-08-2020, 01:20 PM   #9
Rewards Points: 716
You sure you have power to the condenser? The hum may just be the contactor coil.
Old 09-08-2020, 01:29 PM   #10
surferdude2's Avatar
Rewards Points: 896
The diagram is likely correct. Those items you refer to are options that the factory may or may not have installed according to the notes on the bottom there. Those are hard start components not usually needed on most applications.
Your capacitor is shown in that vertical rectangle box and is a dual unit. 40-5 Microfarads.
If you have no meter with a capacitor checker in it, you can do a rough/crude test with a multimeter. The 40 Mfd. section from C to H terminals should show some continuity for a few seconds and then settle down to a zero reading (Infinity). Same for the 4 Mfd. ( C to F) one but much quicker happening. Have the wire/wires disconnected from the C terminal for those tests.
Ah, but I was so much older then...I'm younger than that now
surferdude2 is offline   Reply With Quote
Old 09-08-2020, 03:14 PM   #11
Rewards Points: 42
Roughneck, the noise is not coming from the contactor. The contactor coil operates fine (i.e., sucks in the switch complete when control voltage is applied). I have also confirmed full operating voltage on the load side of the contactor.
Surfer, please see my previous post describing the results of my DMM "ohms only" testing.
I'll pop in the replacement cap in a few days and report back. Not sure that will do it, but I want to eliminate the cap as a possible cause.
Old 09-08-2020, 03:15 PM   #12
Rewards Points: 42
Roughneck, the noise is not coming from the contactor. The contactor coil operates fine (i.e., sucks in the switch completely when control voltage is applied). I have also confirmed full operating voltage on the load side of the contactor.
Old 09-08-2020, 04:17 PM   #13
Rewards Points: 896
I missed that... based on it not going all the way to infinity on the Hermatic and nowhere at all on the Fan, I say you need a new cap. Lucky. The common leg must be flaky... no buldging though. Goes to show they don't always fry and swell up.
Old 09-08-2020, 04:43 PM   #14
A "Handy Husband"
rjniles's Avatar
Rewards Points: 42
Buy a new capacitor and try it, they are cheap- under $20
https://smile.amazon.com/Genteq-97F9...601220&sr=8-13
My electrical answers are based on 2017 NEC, you may have local amendments.