Condenser lines length
Is there a max length of the fluid and vac lines from the condenser to the HVAC unit. I have a AC guy that will hook me up and charge the system. I plan on replacing my old furnace and install a name brand HVAC system that I can buy from the supplier. Thanks
Forrest747 is offline   Reply With Quote
Old 01-27-2020, 05:52 PM   #2
Hvac Pro
yuri's Avatar
Rewards Points: 230
Re: Condenser lines length
Usually 50 feet with the standard size lines that come out of the unit.
You can go longer but then you need to check the manufacturers specs and go with one size larger suction line. That gets pretty expensive.
I usually try keep them under 50 feet. Get a copy of the install manual for the unit and it will tell you what size and how long then can be.
Old 01-27-2020, 05:54 PM   #3
An old Tradesmen
Rewards Points: 122
Yes there is. Each manufacturer has limits that they usually state in the install manual.
How long of a line set were you planning on.
Old 01-27-2020, 06:15 PM   #4
Naildriver
chandler48's Avatar
Rewards Points: 392
The brilliant HVAC engineer who designed the AC system at our church put in 200' linesets. It may not have been all that bad, but he designed in a 40' lift on top of the runs. Totally not within standards. We eventually had to elevate the compressors to the 3rd floor in order to have them operate semi decently.
Larry......
Half of Communications is Listening, and You can't Listen with your Mouth.
chandler48 is offline   Reply With Quote
Old 01-27-2020, 08:38 PM   #5
david86camaro's Avatar
Rewards Points: 4
200 equivalent length is fine for a lot of manufacturers but rise and drop can be very limiting, I think 15 for one and 40-50 for the other depending on the design of the equipment.
david86camaro is offline   Reply With Quote
Old 01-27-2020, 10:04 PM   #6
surferdude2's Avatar
Rewards Points: 932
I installed two 5 ton split system AC's on the roof of an 8 story building that had a KFC kitchen in the basement and the dining area on the first floor. The longest run was approximately 100' so I upsized the lines one size larger than normal. I installed 2 oil trap in the suction risers, one at the bottom and the other at the mid-point. I installed accumulators in the suction line at the high side on each unit.
Everything worked well except the one thing I didn't upsize. I used 18 ga. control wire out of habit and it wouldn't reliably pull in the unit contactors. I repulled #12 wires and all was well. That was in 1984 and the store made it out of warranty and may be still running those units AFAIK.
That's not the longest refer lines I have run but it was the highest. It ran down from the roof alongside the fire escape ladder which made the sil-phos brazing the joints possible once I quit shaking. That building was the former Lankershim Hotel and at least 80 years old, so the fire escape ladder didn't look all that healthy. It's located near the corner of 7th & Broadway in downtown Los Angeles. I think I'll take a look with Google Earth and see if it's still going strong.
Line size at long distances and/or with long risers do require upsizing on occasion but when you do that you are lowering the gas velocity and must address how you get the oil returned to the compressor. Slope is important on horizontal runs but not always possible. It is also important to add additional oil in very long runs. Of course you will need to add additional refrigerant if installing a precharged system.
On other long run systems with multiple pump-down evaporators, we used oil separators since the gas velocity often went so low that the crankcase oil level would go too low if steps weren't taken to prevent it.
If you must err, do it one the side of under sizing the run slightly... it's less risky from a compressor damaging standpoint.
Ah, but I was so much older then...I'm younger than that now
surferdude2 is offline   Reply With Quote
Old 01-27-2020, 11:18 PM   #7
Rewards Points: 932
Holy guacamole! Looks like they're parking cars on that roof now!! The rusty looking rectangle you see there is the metal roof that covered the units I installed. Time has changed things considerably. Parking lot lights also!
The location indicator isn't correctly placed as usual with Google.
Old 01-27-2020, 11:40 PM   #8
Rewards Points: 932
I'm going to bore you even further now. When I installed those AC units in 1984, it wasn't the first time I had been in that building. I stayed in it when it was the Lankershim Hotel and still pretty up scale. That was in 1960 when I was shotgun driver on a 18 wheeler Mack B-61 and a 60' Dorsey refrigerated trailer that my brother and I owned. We stayed there every trip from back east while waiting for our broker to get us a load for the return trip. Usually we hauled ice packed chicken out and oranges, lemons or lettuce back.
Talk about your strange turn of events! It was de javu that second time around but the building was in serious decline at that time and there were so many bums sleeping in the alley behind that it took real care getting our construction trucks through each morning to park without running over one of them. We had to hire a security guard after having the trucks get broken into a few times.
If you're still awake, thanks for reading. If you didn't find it worthwhile, that's OK... I wanted to hear it again.