AC Not Cooling - HVAC - DIY Chatroom Home Improvement Forum
Old 06-10-2020, 10:45 AM   #1
AC not Cooling
Changed from from r22 to 407c. Now the ac not cooling at all.The liquid line is not warm anymore.
Abe22 is offline   Reply With Quote
Old 06-10-2020, 05:55 PM   #2
surferdude2's Avatar
Rewards Points: 898
Re: AC not Cooling
Switching refrigerants can be problematic if not done properly. The oil used in older R22 systems is not compatible with 407C and can gum up the system and plug the metering device and evaporator.. That causes the system to pump down all the refrigerant in the low side to the high side and stop doing any further useful work.
It's so labor intensive and time consuming to get all the old petroleum based oil out of the system that it's usually not worth doing a conversion unless the compressor is being replaced. The replacement compressors have compatible oil in them.
Then it's also possible that you got some contaminant into the system that is causing the problem.
Ah, but I was so much older then...I'm younger than that now
surferdude2 is offline   Reply With Quote
Old 06-10-2020, 07:55 PM   #3
Rewards Points: 716
Re: AC not Cooling
Please describe how you conducted the changeover.
Superheat and subcooling values?
Pressures and temperatures?
roughneck is online now   Reply With Quote