12-2 WG for MINI SPLIT outdoor unit
Will 12-2 WG wire work for MINI SPLIT outdoor unit to breaker box?
bobmane is offline   Reply With Quote
Old 04-21-2020, 04:48 AM   #2
An old Tradesmen
Rewards Points: 124
Re: 12-2 WG for MINI SPLIT outdoor unit
Will on some, not on others.
What size mini?
Old 04-21-2020, 07:00 AM   #3
Rewards Points: 764
May also need some of that wire between the indoor and outdoor unit.
But again, depends on what you have.
roughneck is online now   Reply With Quote
Old 04-21-2020, 09:56 AM   #4
Rewards Points: 172
YMGI 36000BTU12K+24K DUAL ZONE
http://ymgigroup.com/wp-content/uplo...02272020-1.pdf
Old 04-21-2020, 10:51 AM   #5
Rewards Points: 764
Never heard of that brand. But this is in the manual you posted.
12-2 WG for MINI SPLIT outdoor unit-d300c4a7-c0dd-4fcd-b2e8-55b8717fd1b2.jpeg
Old 04-21-2020, 11:15 AM   #6
Rewards Points: 172
Yes in the manual it says 10 AWG and 12 AWG for the bigger unit so 12 would work for this one I assume. I was wondering if 12AWG is the same as the name "12-2 WG" (which is all i could find at home depot).
Old 04-21-2020, 11:55 AM   #7
Rewards Points: 764
The bigger the unit the bigger the gauge wire needed. The smallest unit, the 30, needs the smallest gauge wire, at 12.
WG is just a term for wire plus ground.
What model are you installing?
Old 04-21-2020, 12:57 PM   #8
sktn77a's Avatar
Rewards Points: 1,030
It says 10 AWG (American Wire Gauge) for the 36,000 BTU unit, which is the one in your link. 10 AWG is heavier than 12 AWG. Get the 10 AWG and get a cable for 230v installations - 12/2 is usually for 110v installations.
sktn77a is offline   Reply With Quote
Old 04-21-2020, 02:39 PM   #9
Rewards Points: 172
OK thanks...when you say
do you mean get that in addition to the 10 AWG ?
Old 04-21-2020, 02:56 PM   #10
Rewards Points: 764
The wire voltage rating should be fine.
All the big box stores sell wire that size.
Just remember, no romex outside. You’ll have to get the appropriate outdoor materials to run the wire in.
Old 04-22-2020, 08:36 PM   #11
sktn77a's Avatar
Cable for a 230v system is usually a 10/3, not a 10/2.