-   How To Guides (http://www.diychatroom.com/f98/)
-   -   How to diagnose gas valve problems (http://www.diychatroom.com/f98/how-diagnose-gas-valve-problems-37230/)
Nestor_Kelebay 01-30-2009 11:35 PM
In the "Resources for understanding gas valves" thread in the HVAC forum, someone wanted to know how a gas valve worked. (supposedly so they could fix them :yes: )
The only response he got was to be told to replace them, and NOT to fix them. :huh: (can't win, can ya)
I understood the guy just wanted to know how they worked out of curiosity and so that he could better diagnose problems with water heaters, boiler and furnaces not going on or pilot lights not staying lit.
And, of course, the best way to diagnose a problem with something is to understand how that something works. Then every problem with it is easy to diagnose.
Since this is something EVERY DIY'er should understand, I thought I'd also post the response here as well as in the HVAC forum. Read on...
Darsunt:
Gas valves are actually very simple to understand. Once you understand how they work, it'll almost seem embarrassing to have to explain how they work cuz they're so simple.
When you look at a gas valve, imagine two valves in series.
The gas port where the tube to the pilot light connects is between the two valves, so that gas can flow to the pilot light as long as the first valve, or "safety" valve is open. If the second valve, or "main" valve is open, it can also flow to the burner trays.
Both valves are operated by electromagnets. The electric power to hold the first valve open, and therefore allow gas flow to the pilot light comes from the thermocouple or thermopile immersed in the pilot light flame. The thermocouple or thermopile generates electricity from the heat of the pilot light flame.
So, if the pilot light flame goes out, then the voltage to hold the safety electromagnetic valve open is lost and the safety valve closes, thereby shutting off gas flow completely, including the gas flow to the pilot light.
The second electromagnetic valve in the gas valve, the "main" valve, allows gas flow through a much larger tube to the burner trays. This second electromagnetic valve gets power from either a 24 VAC transformer or the thermopile. Up until recently flue dampers were not required on water heaters so 120 VAC power wasn't needed to operate hot water heaters. As a result hot water heaters typcially used thermopiles to generate more electricity than a thermocouple could, and used that electricity to operate both electromagnetic valves in the water heater's gas valve.
A thermopile is nothing more than about 25 thermocouples all connected in series, so that a thermopile generates about 750 millivolts instead of the 30 millivolts that a thermocouple produces.
On a boiler or furnace, there will be 120 VAC power available to operate the circulating pump or blower, and so by using a 24 volt transformer this 120 volt power can be converted into the same 24 VAC power that the safety controls on a boiler or furnace operate on. By simply putting the second electromagnetic valve in series with all of the safety controls, the second electromagnetic valve will open and allow gas to flow to the burner trays as long as every safety control in that "control circuit" allows power to flow through it. If any safety control detects a problem, it interrupts the circuit to that second electromagnetic valve, thereby shutting off gas flow to the burner trays (but not the pilot light).
This is where I fly off on a tangent:
Typically, the thermostat in a house won't be connected directly to that 24 VAC control circuit to the main valve in the gas valve. That's because to heat up a house you also need the boiler's circulating pump or furnace blower to come on to deliver the heat to the house. I'm much more familiar with hot water heating systems, so I'll describe the typical arrangement for a boiler. Typically the thermostat will be connected to a double pole 24 volt relay, and when that relay gets energized, it completes two circuits; a 120 VAC circuit to the boiler circulating pump or furnace blower, and a 24 VAC circuit through to the temperature control (or "aquastat") on the boiler. When power flows through that aquastat circuit, it energizes a second relay that completes a 24 VAC circuit through all the safety controls to the "main valve" in the gas valve. So, as long as the thermostat is calling for heat, the aquastat is controlling the boiler temperature setting (from 160 to 190 deg. F) and turning on and shutting off the gas valve to maintain the boiler water temperature at that setting. If the first relay completed the circuit to the gas valve directly, then the boiler would keep firing until it kicked itself out on high limit. By having that first relay control a circuit through the aquastat that controls a second relay which operates the gas valve, then the aquastat controls the gas valve to, in turn, control the water temperature in the heating system. A boiler will typically have a "ladder diagram" which shows the start up sequence as sequence of "loops" (kinda like a ladder).
Newer boilers or furnaces will simply have a "controller" that the thermostat connects to that does all this and more.
Back to the chase...
So, to diagnose a gas valve, first check to see if the pilot light is on. If so, then the thermocouple or thermopile is generating enough voltage to keep the safety valve open. If the appliance is a hot water heater but it's not firing up, the thermopile might be weak. It may be producing enough power to open the safety valve, but not enough to open both the safety and main valves together. If replacing the thermopile doesn't work, then you need a new gas valve.
If the appliance is a boiler or furnace, it'll use 24 VAC to operate the "main" valve. Check to see if you're getting 24 VAC at the terminals on the gas valve. If so, and the boiler or furnace isn't firing up, then you need a new gas valve. If you don't have 24 VAC at the gas valve terminals, check for continuity across all the safety devices in the control circuit of the boiler or furnace as it's likely one of the safety devices is interrupting the circuit to the main valve.
The "button" you have to push on a gas valve when lighting the pilot light simply overrides the first electromagnetic valve to allow gas to flow to the pilot light. Once the thermocouple or thermopile is hot enough, the electricity it generates will be sufficient to hold that electromagnet open and you can release that "button". This can often take a few seconds.
Also, thermocouples gradually lose their ability to generate sufficient voltage to operate that safety electromagnet, and when they do, gas flow to the pilot light stops. So, a pilot light that won't stay lit is often the result of an old and weak thermocouple. Different thermocouples get replaced differently. Most of the time you can just pull down on them to pull them out of a spring clip that holds them in place. Other thermocouples will be held in with a thumb screw you loosen from below to pull the thermocouple out. Basically, if it doesn't have a thumb screw on the bottom, pull down on it.
Some gas appliances, like natural gas burning fireplaces will have a "dual" pilot light that has two pilot light flames; one for a thermocouple and the other that continuously heats a thermopile. The thermocouple will produce the voltage to hold the safety valve open in the gas valve, and the thermopile will produce the voltage that goes through the control circuit to the second electromagnetic valve. In this way, the fire place can be turned on, turned up, turned down and shut off with just the turn of a switch even without external electric power being supplied to it.
This is what a thermoCOUPLE looks like:
http://customer.honeywell.com/Honeyw...q340a-c3-3.jpg
The copper "tube" is really a coaxial cable. The outside of the cable is copper and there's an insulated copper wire that runs inside it. When the end of the thermocouple is heated, a voltage is generated between the two copper conductors.
This is what a thermoPILE looks like:
http://customer.honeywell.com/Honeyw...eID=q313-6.jpg
The distinguishing characteristic of a thermopile is that it connects to the gas valve with two electric wires (each with a terminal crimped onto it) rather than with a single nut like the thermocouple does.
And, finally, since both a thermocouple and a thermopile simply create a voltage difference between two wires when their ends are heated, different lengths of thermocouples will all generate the same voltage, just as thermopiles of different length. So you can use a longer thermocouple to replace a shorter one, and use a longer thermopile to replace a shorter one. They're like extension cords or garden hoses or battery booster cables in that respect. That's important to know when you're water heater's pilot light goes out and the hardware store doesn't have a thermopile of the right length. (Just buy a longer one.)
Reilley 02-03-2009 04:55 PM
Cool. I was just wondering about this the other day. Thanks
jackpease 08-18-2009 11:40 AM
testing of the magnetic valve
I found this thread really useful but cannot get my pilot to stay on on my 'millivolt' honeywell system.
I've tested the thermocouple, and it sends out 20-30mv, but the pilot keeps going out when l let go of the white button however long i hold it,
I've undone the spring valve into which the thermocouple goes, and tried to test it, its a very strong spring, how on earth does 20mv hold that spring back - when i've tested it with it makes the spring 'stickier' but not holding it up.
Any hints on testing welcome?
getting an entire new gas valve for a mv system is not straightforward!
thx
jack
HoosierJayBee 03-04-2010 06:12 PM
Thank you for this hard to find information
I consider myself to be an above average searcher on the internet. However, recently when I tried to learn about the internal workings of a furnace gas valve, the only place I found any information was in this forum, at this particular thread. Thanks to Nestor_Kelebay, I finally understand how the gas valve separately controls the pilot light and the main burners.
My furnace gas valve is a Honeywell, and all I could find at their web site was installation instructions and wire drawings.
Thank you Nestor_Kelebay. You might want to consider posting this hard-to-find information at popular web sites such as HowStuffWorks.
avro1 03-07-2010 03:35 PM
1 Attachment(s)
Good info, thanks! I'm wondering though if 750 mv is for all thermopiles.....even my old one dating back to about the mid 50s???
The reason I ask is now and then(mostly now lately) the thermostat won't open the gas valve. If I jump the thermostat terminals on the gas valve with the thermostat closed the valve opens fine and stays open until the thermostat reaches temp and cuts out. I've tried jumping up at the thermostat but the valve still won't open.
It did this once a few years ago so I cleaned the connections and it was good for a few years. Last fall it started acting up again so I cleaned them again but didn't make much difference this time. I just kept jumping those two terminals for a few days and then for some reason it kept working as it should for the winter(got lucky I guess). I'm working on having the furnace replaced but now it's back at it. I checked the thermopile and it puts out about 310 mv with the burner on and about 240 with just the pilot light.
It always seemed to me that the circuit was getting weak and the thermopile was putting out enough voltage to hold the gas valve open but not enough to actually move it due to high circuit resistance(which I fixed) low thermopile output or a gas valve that was just getting old and harder to move.
If ALL thermopiles should put out 750 mv then I see where my problem is but since the furnace is so old I'm not sure if this applies to me. That would be an easy temporary fix until I get the furnace replaced.
Any thoughts?:)
MagicalHome 08-06-2010 01:41 AM
Thanks for that well-descriptive tips. To check for gas pipe leaks, put soap on the pipe connecting to the valve, if it bubbles, it means there's leakage.
Jeanric 10-27-2010 05:01 PM
What about Mechanical thermostats?
Thank you for a very informative description.
Does anyone know where I could get a description (and possibly diagram) of a purely MECHANICAL water heater thermostat/gas valve?
Also, does anyone know if there is an alternative to replacing the whole thing (perhaps replacing a spring or some such small part) when hysteresis (differential) becomes too high? I'm already at my third valve on this water heater, and each time it's a $300 part...
Thank you
jeanric
physicsepv 11-08-2010 10:58 PM
Darsunt:
Great article thanks for taking the time to put this together, it clarified what I had intuitively figured out.
wouldy 09-24-2011 09:40 AM
Outstanding! Now I'm sure my problem's the thermopile.
I have a Hearthstone floor unit which shuts down sometimes -- and evermore frequently. When that happens the pilot light always remains lit. If I stomp on the floor near the unit the burners will relight. From your excellent explanation above, which includes the fact that TWO valves must be open, I surmise that I need to replace the thermopile.
I spent many hours last winter searching (between stomps) for plausible diagnosis of the problem, and I thank you for that.
guyinsb 09-24-2011 01:57 PM
750mv thermopile, gas valve
1 Attachment(s)
Stomping has worked for me as well. The measured output of my thermopile is currently around 350mv; sadly, I failed to get a calibration reading when it was installed (new) a few years ago. So I'm thinking the cause for the valve occasionally failing to open is one of the following:
- pilot light has become too faint (easy to adjust and find out)
- faulty thermopile (a little more work to replace)
- faulty valve (a major pain - my plumber is reluctant to do this)
The expensive option is to replace the boiler and all the controls with a modern system. Certainly the new system will be more efficient,
but the efficiency comes at the cost of complexity and possibly shorter life.
My boiler heats radiator water for a 14 unit apartment in Santa Barbara; it ain't that cold here, and natural gas prices seem pretty reasonable of late.
Can anybody comment on the sanity of just replacing my old General Controls 750mv valve with some equivalent? Any recommendations appreciated.
wouldy 09-24-2011 06:39 PM
Your problem seems to involve large -- really large -- "industrial size" issues. At least having yours done professionally would appear to put you in a position of a tax deduction for repairing it.
Sorry I can't help.
Good luck.
wouldy
wouldy 09-24-2011 06:40 PM
Ever notice how civil DIY'ers are, generally?''
wouldy
doxland 10-02-2011 08:36 PM
Thanks for the excellent tutorial Nestor
I've got a Honeywell Controller in a slide in fireplace.
Pilot lights fine and latches( stays on with flashing LED)
My problem is that switching to main the pilot drops out no matter how long it's been on. I've waited an hour thinking perhaps the thermopile was slow building sufficient voltage.
Any comment on what's going on here?
The pilot's been off all summer and just trying out now.
Pilot color is just plain blue and about 1.5 inches long.
Burning Nat Gas.
False alarm and problem solved.
It was finger trouble
oh'mike 10-02-2011 09:24 PM
Burning Nat Gas.
Please start a new thread in HVAC--Members don't look in to the HOW TO section for questions.--Moderator
davedavidson 12-11-2011 11:42 AM
hvac tech
Darsunt:
And, finally, since both a thermocouple and a thermopile simply create a voltage difference between two wires when their ends are heated, different lengths of thermocouples will all generate the same voltage, just as thermopiles of different length. So you can use a longer thermocouple to replace a shorter one, and use a longer thermopile to replace a shorter one. They're like extension cords or garden hoses or battery booster cables in that respect. That's important to know when you're water heater's pilot light goes out and the hardware store doesn't have a thermopile of the right length. (Just buy a longer one.)[/quote]
How in the h&** do i print this page