Roof/Gutter Deicing Tape - Roofing/Siding - DIY Home Improvement | DIYChatroom
Old 02-11-2011, 07:23 PM   #1
Roof/Gutter deicing tape
I would like to use 2 separate tapes, one for the gutters and a separate tape for the roof edge. I would plug these into a circuit capable of the load. Are 2 tapes ok or should I stay with the 1 tape method?
Davmac78 is offline   Reply With Quote
Old 02-12-2011, 06:09 AM   #2
Residential Roofer
Slyfox's Avatar
The heat cable should run through both the gutters and across the lower roof surface, one piece or two does not matter so long as they are properly installed.
God Family Country Work Play
Facebook <> Twitter
Slyfox Exteriors Co.
Slyfox is offline   Reply With Quote
Old 02-12-2011, 02:25 PM   #3
Low Slope Roofing
Rewards Points: 114
Depends on how long it needs to be. The brand we use can run up to 150 total feet, including D/S drops on one circuit. If you use two they need to be on two different circuits other wise it will trip breakers.
1985gt is offline   Reply With Quote
The Following User Says Thank You to 1985gt For This Useful Post:
Davmac78 (02-12-2011)
Old 02-12-2011, 06:55 PM   #4
Electric Radiant Heating
warmsmeallup's Avatar
Rewards Points: 150
The correct way that will last is to make a double run in the gutter with a loop down the leader and serpentine on the roof dead ending on the end of the roof. Depending on the length, even with two separate cables, you may end up either needing two circuits or one 240v circuit. The 120v Self Regulating cable can run up to 175' (total) on a 30a circuit breaker and the 240v Self Regulating can run up to 375' (total) on a single circuit breaker of 30a. The breakers should also be GFPE (or GFEP) rated breakers. If you plug or connect to a GFCI breaker, you will get nuisance trips from the in-rush.
With double runs everywhere, you have one connection/plug point and enough heat to prevent an igloo that will happen over a single cable run. If you run two separate cables, you need to plug them in separately and, depending on the total length and the voltge cable you use, you may or may not need a single circuit to run them.
www.comfortradiant.net
warmsmeallup is offline   Reply With Quote
Old 02-12-2011, 07:24 PM   #5
Low Slope Roofing
Rewards Points: 114
Take a look at this.
http://www.tycothermal.com/usa/engli...m/default.aspx
and this
http://www.tycothermal.com/assets/Am...esign_1110.pdf
Should be all you need to decide how many cables you need.
Old 02-12-2011, 07:27 PM   #6
Low Slope Roofing
Rewards Points: 114
You can do it with one cable. You just cant go over your total lenght limit. That is determined on how many watts per foot of cable, circuit size and min temp. 175' would be MAX in the best of conditions. Last ones I did were 150 each circuit, and that was pushing it with an 6 watt per foot cable.
Old 02-12-2011, 09:09 PM   #7
Rewards Points: 150
So, here's the math...Self Regulating wire in "the worst case scenerio, zero degrees" is 12 watts per linear foot. If you have a 120v circuit and 175 linear feet of cable (175' x 12 watts = 2100 watts), take 2100 watts and devide by 120 = 17.50 amps. So, 175' of SR cable at 12 wpsf will run comfortably on a 30 amp circuit considering the in-rush, no problem. We don't use the 6 watt stuff in the north east. It bridges over too easily.
Do the same calculation for 240v cable and you get 18.5 amps...375' no problem!
Old 02-12-2011, 09:14 PM   #8
Low Slope Roofing
Rewards Points: 114
Never have had problem with 6watt tape. Never have installed any for 220/240 hard enough to get them to put a regular outlet near by.
Old 02-13-2011, 08:49 AM   #9
Rewards Points: 150
We don't install 'plug in' systems. I sell the materials for others to do that work. We install the efficient ones that use SR cable and connect to a junction box and use a temperature/moisture sensor that activate/deactivate themselves.
I stay away from the 6 watt cable. It's not that I think it's bad..it just doesn't work well enough in the northeast.
Old 02-13-2011, 03:33 PM   #10
Low Slope Roofing
Rewards Points: 114
The "plug in" systems we install are a self regulating cable also, you can hard wire it to a junction box. You can use a temp/moisture sensor also. Its just they have a handy gfci on the plug in it's self. Also you do not need a temp/moisture sensor with the systems, they just save you $$.
Old 02-13-2011, 05:42 PM   #11
Rewards Points: 150
I misunderstood you when you said that you use 6 watt cable. The MI cable is 6 watts (some of them are 5) but they are one wattage all the time. That's the cable I was refering to that we don't install. Yes, if you are using SR cable it is efficient in that it starts at 6 watts unless you plug it in when they're covered in snow.
Old 02-13-2011, 05:50 PM   #12
Low Slope Roofing
Rewards Points: 114
Rey Chem is the brand we use. Yes it starts at 6watts. I think its like 50 degs or so, then it goes up from there depending on load and what not.
Effects of electrician tape on cable richard7994 Electrical 4 08-11-2010 08:39 AM
Paint problems....or just problems with the painter... deanswife Painting 5 07-30-2010 08:36 AM
Aged Painting Tape Needs to Come Off user1007 Painting 2 03-04-2010 05:16 PM
Frozen Hot Water Pipes TravisW Plumbing 11 12-10-2009 05:26 PM
Masking and Blue tape ripping off paint LeviDIY Painting 20 10-21-2009 06:56 PM