I think my attic ventilation is inadequate because on hot summer days the second floor is 10+ degrees warmer than the first floor. An hour or so after dusk the second floor cools off, but it's never as cool as the first.
One problem I know I have is the whole house attic fan is as air tight as a sieve when not in use. The hallway where it's located is extremely warm on hot summer days. I'm making an insulated cover for it that should help.
The attic is approximately 1000 ft^2. I have a gable roof and one side of it are six roof louvers. On the same side of the house as the louvers there are four 8x16 undereave vents. According to some information I found online, I calculate my current NFA as the following:
For a 1000 ft^2 attic, the my total current NFA seems adequate.
Required NFA = 1000 ft^2 / 300 * 144 = 480 in^2
524 in^2 > 480 in^2
I wouldn't be surprised if my intake vents are currently partially blocked. Last fall, in preparation for adding more insulation to the attic, I installed rafter vents. While doing this I may have pushed some blown in insulation onto the inside of the vents.
The first thing I should probably do is get up on a ladder, remove the vents, and clear away any obstruction. From information I've found online, I might also need to add more vents because my intake NFA is lower than my exhaust NFA.
Ultimately, I would like to add an exhaust fan to (at least) one of the louvers. The problem here is that no one seems to make fans that can be added to a louver. I guess I could just replace one of the louvers with a powered vent, but I'd rather not get up on the roof.
Above 30 Air Changes per Hour seems like the point of diminishing returns for attic ventilation and some recommend as little as 5 ACH.
I'd make before-and-after temp. measurements in the attic to see what you're up against. Take the average of several readings.
It seems that builders have long ago forgotten a basic physical reality: Things that are less dense rise... like hot air.
I've never met the original poster before, nor been to it's home. But I will now reach out with my incredible mind and tell you astounding details about it's house!
Ready to be amazed?
1. The stairway from the first floor to the second floor is completely open.
2. The thermostat for the home is located in an out of the way spot on the first floor.
3. In the summer, the upstairs it too hot while the downstairs can sometimes seem too cool... in the winter the same is true.
Cold air is like water. It will flow down and pool at the lowest level of the house it can. Same for hot air, but upside down - it will pool in the highest parts of the house.
While your attic might be hot, it is Unconditioned space... let it be hot. You only care about the floor of the attic where you insulate. All you really need to do is seriously insulate the attic floor, but that will only keep the heat from going down into the second floor. It does nothing for the heat already IN the house from traveling and pooling on the second floor.
A couple of strategies for you:
1. Get a programmable thermostat that has a function allowing you to run the fan alone at periodic intervals independent of temperature. Say 5 or 10 minutes of fan every hour. This will keep the hot and cold air mixing.
2. Put a door at the top or bottom of your stairway. This will keep your hot/cold pools separated into two different zones. Grand open stairways were great tools for moving air in the days before closed windows and HVAC. Now they are an architectural relic that only serves to look pretty and make us feel miserable.
3. Move your thermostat into an area that more closely resembles a living space. If there is one room downstairs that is hot when the upstairs is hot, that is where you want the thermostat.
Hot air rises and cool air sinks. I can't believe I've gone several decades without realizing that. You would think that someone who takes it upon themselves to do their own house repairs and even seeks out the best way of doing so would have come across that basic principle of physics by now.
I realize there are other things I need to do and can do inside the house. My focus right now (and the purpose of my original post) is attic ventilation.
I think air infiltration is the worst thing here. If you go around your attic with a tube of caulk and can of spray foam, you can do a lot to keep the hot air from coming into your house. Every pipe or wire that comes thru the top plate needs to be sealed around. Every electrical box in the ceiling needs a layer of spray foam over it like a cocoon. When I replace ceiling fans I can't tell you how much air I get blow in my face from the canopy, it comes right thru all those little holes in the electrical box and into the house, dust and insects too. Any high hat needs to be replaced with an airtight IC rated model.
Having the living area of the house sealed off from the attic is the main issue. After that, a layer of good insulation will be enough. I do a lot of electrical work in attics, it will be 130 degrees up there yet I pull up a measly piece of R-19 insulation and the metal electrical box will be cool to the touch, most of the heat is going UP, not down into the house. Having good ventilation might help your home a bit, but not THAT much. It will help your roof quite a bit, tho. You also need some ventilation to keep the moisture at bay.
I spent many weekends last fall doing this very thing. Every crevice and hole I could find got filled with caulk or foam. I even replaced all my old recessed lighting fixtures with new ICAT fixtures. I did all of this in preparation of adding insulation, but I still haven't gotten around to it.
Looks like getting the extra insulation in needs to be my primary goal.
suggestions to what? you seem to have more than required venting,your gonna fix the intake vents you screwed up,your not going on the roof,your gonna make an insulated cover for the leaky fan one day...i think your doing fine:whistling2:
"On the same side of the house as the louvers there are four 8x16 undereave vents." ------- So all intake are on one side of a gable house? What intake is on the other side?
And you do know when figuring the NFVA to divide by 300 WITH a vapor barrier installed between ceiling/insulation, otherwise use 150....... And that is with plastic, not a vapor retarder paper on the insulation: http://www.airvent.com/homeowner/products/intakeSoffit-specs.shtml
"Yes, all on one side. No intake on the other side, at least none that I can see on the undereave." ------ Is there room to install intake vents on the dead air side? Either continuous or roof mounted?
Yes there is. I'm now planning to install 8ft undereave soffit strips.
In an earlier post you made you included a link to a document that concluded powered exhaust vents may do more harm than good because they can draw conditioned air out of the house. If I've already sealed everything I could get to in the attic, and if I install enough intake ventilation, will this minimize the chance that an exhaust fan would draw conditioned air from the house?
I agree w/Paul in that a programmable t-stat would be better. Moving it to a wall that will get some of the conditioned air. If the stat is in an 'out-of-the-way' spot, there will be no air getting to it to close the loop--that's why your downstairs is always cold. If you don't have a separate upstairs unit, that area will always be hotter. I'm a big fan of radiant barrier foil, which I installed a couple yrs. ago in our attic. Big difference, as it keeps the hot air out --which keeps ductwork and conditioned air cooler.
Is there any way to balance the system to get more air flow upstairs to try and compensate?
Only way to get more air upstairs is possibly closing off some downstairs registers, but many say this does more harm than good. If you could install levers that close off the duct where it comes off the main duct line in the attic, that would work better. Shutting off registers in rooms will just divert to next closest vents/rooms. Another idea may be decreasing duct size downstairs, but that's a difficult option, if not impossible. Of course, using ceiling fans upstairs will help. Is your AC tonnage adequate?
May need to get a new unit installed.
No, the attic foil is great. I really don't think dust has any effect on it, and probably is BS you'll hear from the RB spray-on guys. If you look at the site, http://www.atticfoil.com you'll see it's tacked up on the studs--leaving a 3 to 4" gap that traps the hot air and move it upwards. You must have adequate vents to remove this heat (ie. SOFFITS and ridge/turbines/powered fans/etc.) That's the best way to install it. The easiest way is just to lay it over the insulation, but your attic and ductwork still gets really hot.
This is what I'd do if I were you. Keeping the heat OUT in the first place is much easier than overworking your AC unit every summer. I don't run our AC's during the day, I have them set to go off when we leave for work.
But when we got home at 5pm or so, our house is never over 80*. Then the air kicks on and cools it down in an hr. or 2.
Our last house in Illinois was a colonial with AC. Big problems keeping the upstairs cool. I purchased magnetic vent covers that blocked most air flow in the downstairs vents so all the cold air would have to start out UPstairs before it could cool the downstairs. That made a real difference in balancing the system out. I reversed it in the winter for hot air flow.
I had one floor vent in the bathroom that must have been the first vent off the HVAC system. When I blocked the downstairs vents, and the blower kicked on, it would literally BLOW the vent out of the floor! I had to obstruct that vent channel just so I could keep the vent on the floor!
“the chance that an exhaust fan would draw conditioned air from the house?” ---- Do you have a plastic vapor barrier installed at ceiling/attic joint? OR a vapor barrier primer paint rated at 0.05 permeability on the whole ceiling?: http://www.panhandleinsulation.com/buildingmaterials.html
Hot air goes up. if you open your doors & blinds it doesn't matter how much insulation you have. Window glass (double glazed with argon gas) is only about R4.
If you have a real problem upstairs with heat there are several ways to cool off the rooms.
First one (& my kids used to laugh at me but all do it now)
keep the cutains drawn during the heat of the day, as it cools off pick an upstairs window & put a fan in it blowing out at high speed.
Close your downstairs doors & windows
Open your upstairs windows in the rooms you want to cool off
Close the doors in those rooms to within about 2 inches(you may need to put something in the door to stop the air from closing it)
The fan draws the cooler air through the window and the door but because of the restriction of air to 2 inches, air is drawn from the ceiling as well as the floor
Takes about 1/2 hr to cool off a room.
Second- yes a 2 speed fan works but you need a return air on the ceiling or close to it otherwise your just blowing hot air around.
Third- opening skylights are a great way to remove the heat
Forth-Most people don't realize how good cedar shakes are at insulating from the heat before it enters your attic
Hope one of these solutions work for you
Dale Chomechko
DC Roofing Inc
Fine Home Building magazine just had an article this month about "Stack Effect", good reading, though I'm not sure I buy into all the items presented.