11-25-2012, 12:28 AM
#1
Framing inspection failed due to roof
County inspector failed framing on my garage because the 7/16 OSB sheathing on 24" centers for the roof did not have plywood H-clips. He said an acceptable fix would be to install 2x4 blocking at all plywood seams.
This is fine, but it ruins my plan for insulating the roof with fiberglass, using the foam baffles to leave an air gap for ventilation from the soffit to the ridge vent. The main problem being that what would have been a 2" air gap, will now be reduced to 0.5" because of the installed blocking.
Are there any alternatives to the blocking that I could use? Perhaps something with steel that I could affix to the underside of the seams?
Thanks.
11-25-2012, 12:50 AM
#2
H clips might work
Sounds like inspector may be helping you out here.
H clips add a expansion joint between the osb, those little clips do not really give you support on seams when walking on roof.
I f you butted the osb up tight with no clips, in future the osb will expand and contract, causing the joints to buckle .... may not cause your roof to leak, but can look like crap very quickly.
By adding the 2x4 blocks underneath, may be able to control this ... but just using H clips in first place would have been better.
So inspector feels your pain, gives you an alternative that may work without forcing you to tear the sheathing off and redo it .... and you are asking for a easier way?
At this point, do what the inspector tells you, anything else and he may make you tear it off and do it right.
If it was easy, we would not call it work!
11-25-2012, 01:17 AM
#3
Funfool: Thanks for replying, but you're making some incorrect assumptions here. This is a contractor who built this garage for me, one which is well known and well established.
Re-read my post carefully.
I would rather the inspector require me (rather, the contractor) to tear off the roof and do it right. The fact that the inspector gave leeway with the blocking is throwing a wrench into my plans for insulation - which I am DIY'ing.
What I'm asking is if there's any other way besides blocking to correct this - preferably a method which would still allow me to maximize my R-value and required ventilation gap under the roof deck.
Hope this clears up the confusion.
11-25-2012, 01:26 AM
#4
Exterior Construction
run some 2" by 2" battens vertically on the roof at the seam and still put the blockers in there horizontally. This will preserve the vent space and still support the seams of the plywood.
11-25-2012, 02:24 AM
#5
JOATMON
How about drilling some 1" holes in that blocking so the air can get by. I'm assuming you would use boundry nailing...which is typically 6"...so that gives you some room to put in 2-3 holes.
Just as a side not......if the contractor is so well respected.....7/16" OSB 24" OC? Are you kidding? I don't think I have seen a roof done with 7/16" OSB where it was not sagging....16" OC is marginal...but 24"? The blocking is going to help a lot with the sagging....be glad the inspector wants it.
I did a lot of research on OSB vs plywood for roof....from what I can tell, Plywood is by far much better for a roof.
Common Sense is like Deodorant. Those that need it the most don't use it.
My To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. ... To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. and To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
11-25-2012, 04:06 PM
#6
shouldn't the contractor be responsible for doing thing to code?
The Following User Says Thank You to terry603 For This Useful Post:
11-25-2012, 04:12 PM
#7
Using H clips is roofing 101, I'd make the so called contractor redo the roof at no charge.
11-25-2012, 06:53 PM
#8
Moderator
If the panel rating is 24/0, you need the blocking or clip, if 24/16---- not required, check the panel ink stamp in the attic...unless it is a local code amendment. http://www.apawood.org/pablog/index....Roof-Sheathing
http://publicecodes.cyberregs.com/ic..._23_par100.htm
http://www.strongtie.com/products/co.../pscl-psca.asp
Gary
P.S. the air channel is for cathedral raked roofs, not insulated attic floor, I may not understand your application.
Clothes taking longer to dry?
11-25-2012, 08:00 PM
#9
Thanks for the super-helpful post, GBR. It is stamped 24/16. Maybe the inspector missed that. Ill double check.
The garage has a narrow 10 foot attic area in the center of the trusses, but is otherwise open to the rest of the garage. I plan on using tools in the space, so i want it conditioned. In other words, it will have a cathedral ceiling.
11-25-2012, 08:44 PM
#10
Moderator
You are welcome. If you don't need them, you could make your own baffles; http://www.buildingscience.com/docum...n-roof-venting
The plastic baffles are better than the foam ones that rip on the protruding nails in the roof sheathing. With insulation touching these types/styles baffles, you get thermal conduction= loss of R-value. The rigid foamboard also stops insulation wetting from "night-sky radiation"; http://www.buildingscience.com/docum...bout-diffusion and leaves all the roof sheathing open/exposed to air flow to remove moisture.
Gary
11-26-2012, 06:56 PM
#11
RFN-4A-LVN
If the garage isn't that big and the roof isn't installed.Mark 1/8" off the seam,,pop a chalk line,,set your saw,cut the 1/8" along the seam,,bend one side of the clip flat,,insert,,then flatten the clip.
11-27-2012, 10:52 AM
#12
If your contractor is so well established why did he make such a rookie mistake? Make him come back and fix his mistake at his expense. It is his responsibility to do the work to local code. I would be ashamed to leave my customer with this kind of mess.
-Grumpy
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
Sometimes the savings that comes from doing it yourself can be blown away with one mistake.
The information found in this post is not to be considered legal advice. All information should be considered relative, not specific. Never attempt any repairs you are not comfortable with. Always maintain safety! The author of this post takes no responsibility for any losses that occur. Use at your own risk.
11-28-2012, 01:04 AM
#13
Residential Designer
It sounds like an un-vented attic assembly is the best way to remedy this.
Andy.
Residential Drafter/Designer
11-28-2012, 06:13 AM
#14
Super Moderator
This is a DIY site---there is no 'contractor' just a homeowner that is learning and seeking help----
Be helpful---Mike-----
11-28-2012, 10:45 AM
#15
Andy, presuming you mean spray foam insulation on the bottom side of the sheathing when yous aid "unvented attic assembly" that may be the quickest way to please the building inspector after installing the braces the inspector had requested. However won't do anything for sheathing buckling if no spaces were left between the sheets, and also could also possible void and/or limit some shingle manufacturer's shingle warrantys.
oh' Mike the original poster stated he had hired a contractor to build the garage. So the question remains, why is the original poster accepting sub standard work for his/her money invested? Why now does the original poster want to now DIY repair something the contractor, to whom I presume was paid, screwed up?
That is akin to buying a brand new car from the show room floor of a new car dealer, and rebuilding the engine the day you take it home because the engine is knocking.
-Grumpy
| Thread Tools |