novaguy 11-25-2012 12:28 AM
County inspector failed framing on my garage because the 7/16 OSB sheathing on 24" centers for the roof did not have plywood H-clips. He said an acceptable fix would be to install 2x4 blocking at all plywood seams.
This is fine, but it ruins my plan for insulating the roof with fiberglass, using the foam baffles to leave an air gap for ventilation from the soffit to the ridge vent. The main problem being that what would have been a 2" air gap, will now be reduced to 0.5" because of the installed blocking.
Are there any alternatives to the blocking that I could use? Perhaps something with steel that I could affix to the underside of the seams?
Thanks.
funfool 11-25-2012 12:50 AM
H clips might work
Sounds like inspector may be helping you out here.
H clips add a expansion joint between the osb, those little clips do not really give you support on seams when walking on roof.
I f you butted the osb up tight with no clips, in future the osb will expand and contract, causing the joints to buckle .... may not cause your roof to leak, but can look like crap very quickly.
By adding the 2x4 blocks underneath, may be able to control this ... but just using H clips in first place would have been better.
So inspector feels your pain, gives you an alternative that may work without forcing you to tear the sheathing off and redo it .... and you are asking for a easier way?
At this point, do what the inspector tells you, anything else and he may make you tear it off and do it right.
novaguy 11-25-2012 01:17 AM
Funfool: Thanks for replying, but you're making some incorrect assumptions here. This is a contractor who built this garage for me, one which is well known and well established.
Re-read my post carefully.
I would rather the inspector require me (rather, the contractor) to tear off the roof and do it right. The fact that the inspector gave leeway with the blocking is throwing a wrench into my plans for insulation - which I am DIY'ing.
What I'm asking is if there's any other way besides blocking to correct this - preferably a method which would still allow me to maximize my R-value and required ventilation gap under the roof deck.
Hope this clears up the confusion.
Windows on Wash 11-25-2012 01:26 AM
run some 2" by 2" battens vertically on the roof at the seam and still put the blockers in there horizontally. This will preserve the vent space and still support the seams of the plywood.
ddawg16 11-25-2012 02:24 AM
How about drilling some 1" holes in that blocking so the air can get by. I'm assuming you would use boundry nailing...which is typically 6"...so that gives you some room to put in 2-3 holes.
Just as a side not......if the contractor is so well respected.....7/16" OSB 24" OC? Are you kidding? I don't think I have seen a roof done with 7/16" OSB where it was not sagging....16" OC is marginal...but 24"? The blocking is going to help a lot with the sagging....be glad the inspector wants it.
I did a lot of research on OSB vs plywood for roof....from what I can tell, Plywood is by far much better for a roof.
terry603 11-25-2012 04:06 PM
shouldn't the contractor be responsible for doing thing to code?
joecaption 11-25-2012 04:12 PM
Using H clips is roofing 101, I'd make the so called contractor redo the roof at no charge.
Gary in WA 11-25-2012 06:53 PM
If the panel rating is 24/0, you need the blocking or clip, if 24/16---- not required, check the panel ink stamp in the attic...unless it is a local code amendment. http://www.apawood.org/pablog/index....Roof-Sheathing
http://publicecodes.cyberregs.com/ic..._23_par100.htm
http://www.strongtie.com/products/co.../pscl-psca.asp
Gary
P.S. the air channel is for cathedral raked roofs, not insulated attic floor, I may not understand your application.
novaguy 11-25-2012 08:00 PM
Thanks for the super-helpful post, GBR. It is stamped 24/16. Maybe the inspector missed that. Ill double check.
The garage has a narrow 10 foot attic area in the center of the trusses, but is otherwise open to the rest of the garage. I plan on using tools in the space, so i want it conditioned. In other words, it will have a cathedral ceiling.
Gary in WA 11-25-2012 08:44 PM
You are welcome. If you don't need them, you could make your own baffles; http://www.buildingscience.com/docum...n-roof-venting
The plastic baffles are better than the foam ones that rip on the protruding nails in the roof sheathing. With insulation touching these types/styles baffles, you get thermal conduction= loss of R-value. The rigid foamboard also stops insulation wetting from "night-sky radiation"; http://www.buildingscience.com/docum...bout-diffusion and leaves all the roof sheathing open/exposed to air flow to remove moisture.
Gary
Roofmaster417 11-26-2012 06:56 PM
If the garage isn't that big and the roof isn't installed.Mark 1/8" off the seam,,pop a chalk line,,set your saw,cut the 1/8" along the seam,,bend one side of the clip flat,,insert,,then flatten the clip.
Grumpy 11-27-2012 10:52 AM
If your contractor is so well established why did he make such a rookie mistake? Make him come back and fix his mistake at his expense. It is his responsibility to do the work to local code. I would be ashamed to leave my customer with this kind of mess.
AndyGump 11-28-2012 01:04 AM
It sounds like an un-vented attic assembly is the best way to remedy this.
Andy.
oh'mike 11-28-2012 06:13 AM
This is a DIY site---there is no 'contractor' just a homeowner that is learning and seeking help----
Be helpful---Mike-----
Grumpy 11-28-2012 10:45 AM
Andy, presuming you mean spray foam insulation on the bottom side of the sheathing when yous aid "unvented attic assembly" that may be the quickest way to please the building inspector after installing the braces the inspector had requested. However won't do anything for sheathing buckling if no spaces were left between the sheets, and also could also possible void and/or limit some shingle manufacturer's shingle warrantys.
oh' Mike the original poster stated he had hired a contractor to build the garage. So the question remains, why is the original poster accepting sub standard work for his/her money invested? Why now does the original poster want to now DIY repair something the contractor, to whom I presume was paid, screwed up?
That is akin to buying a brand new car from the show room floor of a new car dealer, and rebuilding the engine the day you take it home because the engine is knocking.