Old 06-24-2007, 12:14 PM   #1
I have gas!
Clutchcargo's Avatar
Water heater flue gas condensation problem?
I had this water heater installed in Oct '06. I noticed there's a bit of flue gas condensation on top of it and it's rusting there as well. Is this a problem or is this typical?
TIA
I tear things down and build them up.
Clutchcargo is offline   Reply With Quote
Old 06-25-2007, 08:59 PM   #2
I have gas!
Is it possible that flue gas is escaping around the outside sleeve? I have to admit that I really don't know much about the anatomy of a water heater.
Old 06-26-2007, 06:32 AM   #3
Union HVAC Tech.
Wrong set up, the flue from the water heater is supposed to enter the chimney higher than the boiler flue. The way it is, on a warmer day the flue gases from the boiler will spill out when it fires up before you start to draft properly. Flue gases will follow the path of least resistence (ie spill out the draft hood). Also check the static (non-firing) draft pressure.
bigMikeB is offline   Reply With Quote
Old 06-26-2007, 01:21 PM   #4
I have gas!
Are you saying there should be two flues entering the masonary chimney and they connect further up the chimney?
Old 06-26-2007, 09:59 PM   #5
Union HVAC Tech.
On a horizontal breeching such as yours, there should be two pipes entering the chimney, the smaller appliance being the higher connection. They don't need to have space in between them, one can sit directly on the other.
No Expansion Tank for Water Heater vasanvasan Plumbing 4 12-14-2007 12:16 AM
How to Space Water Heater Flue Vent from Outside Wall? austinbirdman Plumbing 1 03-12-2007 11:28 AM
Periodic release from (I think) the T&P valve on the water heater alexz Plumbing 3 08-15-2006 11:31 AM
Draining a hot water heater singforsupper Plumbing 1 06-07-2006 07:01 PM