Hello - we need to update our sump pump, so had a contractor come and take a look.
He noted that the water level in the sump is well about the drain tile inputs by the time the pump kicks in. When the pump triggers and the level goes below those inputs, the flow into the sump is substantial until the level goes above those inputs, and then it seems to slow down again.
But he made a claim that the water level in the drain tiles could be much higher than in the sump. That sounds like nonsense to me: when the sump is filling slowly, it's almost a hydrostatic situation, and the water level is very nearly the same throughout the system.
Also, his solution is to do ~$1100 worth of work to extend the sump pit down about 14 inches, which sounds pretty disruptive to our finished basement.
Question 1: is his claim about the higher water level in the drain tile suspect?
Question 2: Are there other solutions besides extending the sump pit? For example, changing pump on/off limits?
Many thanks,
Pat
pnorman55 is offline   Reply With Quote
Old 03-17-2016, 12:20 PM   #2
Civil Engineer
Rewards Points: 4,568
Re: Sump water level
If you understood his claim correctly, it is nonsense. The level in the drain tiles will be essentially the same as the level in the sump pit, unless the pump is running. You are correct, the water flow is so slow that the velocity head in the water is negligible, and the levels are the same.
I am unclear from your post what the problem is that you are trying to solve. My sump pit is about 14 inches deep (relative to the basement floor), which is pretty typical. Some are a little deeper. My sump pump float is set to turn on when the water level gets to about four inches below the floor, so there is about 14 inches of water in the sump at turn on. The pump turns off when there is about 6 inches of water in the sump, so the pump drawdown is about 8 inches. This means that I allow the water level in the sump to get to within four inches of the floor before the pump turns on. This is not a problem, remember the only purpose of a sump pump is to keep the basement floor dry, so there is no point running the pump needlessly when the level is well below the floor (4 inches in my case).
Conclusion: You may not have a problem, perhaps you have an old pump, in which case replace it. I would not make the sump deeper unless there is some other problem you have not described.
The Following User Says Thank You to Daniel Holzman For This Useful Post:
oh'mike (03-19-2016)
Old 03-17-2016, 12:48 PM   #3
Rewards Points: 18
Thanks for your response!
I'm not sure there is a real problem, except that the drain tile never completely empties. But that might be because our sump discharge drain has been poorly functioning for a while, and I think the discharge has been coming right back to the foundation. That in turn means there's not much buffer between the water level in the sump and the floor. There's a backup, but it will only trigger when the sump is almost overtopped. I think a little more margin of safety would be good, but maybe it's not needed?
I've run a temporary discharge on the surface well away from the house, so hopefully the inflow rate will drop and the drain tiles will clear.
Old 03-17-2016, 02:03 PM   #4
Civil Engineer
I still don't understand what the problem is. Drain tile is usually set well below foundation level, often 12 inches or more. So the drain tile will not drain completely unless the water table is lower than the bottom of the drain tile. If you set your float to turn on when the water level reaches four inches below the floor elevation, then during the wet part of the year the drain tile will not drain completely. This is NOT a problem.
What is a problem is that you think the sump pump does not empty to the street, a storm drain, or something similar, but instead cycles the water back to the foundation. This is incorrect, and needs to be addressed if it is the case. My drain tile does not drain completely most of the year, but the pump only turns on a few days a year, when the water table is reaches closer than four inches below the floor. Much of the rest of the year, the water table is between 14 inches below floor level and 4 inches below floor level, so there is water in the sump pit, the drain tiles are full, but there is no need to run the pump. This is NOT A PROBLEM, and if you have a similar situation, you don't have a problem either. Just make sure your pump drains correctly, test your pump monthly, and make sure your pump is adequate to keep up during heavy rainfall events.
The Following 2 Users Say Thank You to Daniel Holzman For This Useful Post:
oh'mike (03-19-2016), pnorman55 (03-17-2016)
Old 03-17-2016, 02:06 PM   #5
Rewards Points: 18
Thank you for the very clear answer - I understand now that the water level per se is not a problem. Good to know.
I definitely understand that the poor discharge is a problem, and we're having that fixed.
Thanks again!
Old 03-17-2016, 05:53 PM   #6
Rewards Points: 1,770
712.3.4 Maximum effluent level.
The effluent level control shall be adjusted and maintained to at all times prevent the effluent in the sump from rising to within 2 inches (51 mm) of the invert of the gravity drain inlet into the sump.
Old 03-17-2016, 06:07 PM   #7
Rewards Points: 18
So, in everyday language.... the pump should kick in when the water rises to within 2 inches of the drain tile input to the sump?
By the way, I see that your quote is from the International Plumbing Code chapter on Sanitary Drainage. Does that apply to a non-sanitary sump?
Thanks.
Old 03-17-2016, 06:27 PM   #8
Civil Engineer
You have a storm drain pump, not a sewage pump. I see no relevance of a quote on sewage pumps.
Old 03-17-2016, 08:25 PM   #9
Rewards Points: 1,448
For best performance of the drain tile, there must be an air pocket all the way around the route of the drain tile. Exactly how much the drain tile end can be submerged without eliminating the air pocket at the opposite wall of the basement depends on the slope of the drain tile.
You may or may not have basement flooding problems with your sump pump floats set the way they are. But if the air pocket is missing in places, then it is possible for the basement floor to get flooded while the level of water in the sump is well below floor level.
The suggested starting point is for the pump to turn on before more than half of the drain pipe ends are submerged. (Local code may require the pump start level to be lower.) Should you get flooding at the far side of the basement, adjust the pump turn on level to be lower still but let it run with the new setting for a week to let the soil under the floor desaturate before drawing conclusions whether your new setting is good enough.
It is best for the sump to be emptied out as much as possible before the pump turns off again. If it takes a long time for the water level in the sump to rise between rainstorms or if the water level sits still and quite high between pump restarts for days and days, that is okay.
If you are digging a new perimeter drain tile system for an existing basement, do not dig below the level of the bottom face of the foundation footings at the footings.
The advantage of optionally extending the pit downward is to allow more water to accumulate between pump starts. Fewer longer pump cycles are better than many shorter pump cycles.
Old 03-17-2016, 09:47 PM   #10
Rewards Points: 18
That makes sense, and maybe explains what the contractor was claiming.
Thanks much.
Old 03-18-2016, 09:54 AM   #11
Rewards Points: 242
The basement in my old house had this problem. We had a very high water table. The pump would kick on, empty the pit, and be followed by a rush of water out of the filled drain tiles, which would slow as the pit refilled. This was year-round except for maybe 1-2 months during the summer.
I lived there 20 years without any water seepage into the basement. The rush of water was pretty loud, and I did go through a lot of sump pumps because of the constant recycling. Other than that it never seemed to cause any problems.
Any chance you could find another pump with an adjustable switch? This might allow you to have the pump kick on sooner. However, that will probably just increase the frequency of your pump cycling.
b-boy is offline   Reply With Quote
Old 03-18-2016, 10:54 PM   #12
My own recommendation is for the sump to have 3 cubic feet (a little over 20 gallons) of space below the drain pipes and not filled with rocks and gravel. You would have to custom pour a concrete sump or build it with bricks since very few plastic sump liners are that size. An existing small sump is probably also small enough in diameter that retrofitting it with more volume deeper down and lining it to prevent cave in is very difficult.
A larger volume of accumulated water means the pump is working on it for more time. This also gives more time for the tremendous rush of queued up water in the drain pipes to come into the sump and be pumped out during the same cycle rather than have to wait until the next cycle
Except that accumulating more water by letting the water level go higher runs the risk of eliminating the air pocket here and there around the drain tiles and then run the risk of flooding the floor at the opposite side of the basement.
Old 03-19-2016, 03:46 PM   #13
So your good with undermining the foundation?
Old 03-19-2016, 03:58 PM   #14
Thanks.
No it doesn't my mistake.
Old 03-19-2016, 06:43 PM   #15
Civil Engineer
I have no idea where the theory that you need an air pocket in a perimeter drain for it to function correctly comes from. I have designed more than 10 perimeter drain system for commercial buildings, and I have a drain system in my house. None of the system I have designed have included an air pocket, and they all worked just fine.
There are only a few requirements for a drainage system to function correctly.
1. The drain pipes need to be perforated with the holes down to collect the water. They should be packed around with crushed stone and filter fabric to keep out the fines.
2. The drain pipes need to be flat or pitch slightly downhill to the sump. I normally lay the pipes flat.
3. The pipes need to be sufficiently below the floor level to maintain the water table at the desired elevation, typically 6 - 12 inches below the floor level.
4. The sump pit should be large enough to prevent short cycling of the pump.
5. The pipes can run into the pit at any elevation. Mine run into my pit about 10 inches below floor level. My pit is about 14 inches deep. My pump does not turn on until the water is about 4 inches below floor level, and it turns off with about 6 inches of water left in the sump pit. This prevents the pump from overheating, as most submersible pumps are not designed to drain the sump dry.
Maybe someone can explain the physics behind the claimed need for an air pocket in the pipes, when my pipes are running, there is no air in them, and they work just fine, as have all the other systems I have designed.
oh'mike (03-20-2016)
Tags
drain tile , drainage , pump , sump
Sump pit keeps filling, can't see water coming in ks-man Plumbing 30 12-31-2014 06:32 PM
Chasing Ghosts - Phantom Water Leak FrozenMeatballs Plumbing 7 10-29-2014 07:03 PM
Sump Completely Dry but Found water in basement? thefish7 Plumbing 3 08-09-2011 12:13 AM
Sump hole and water drain questions Ncasalejr Plumbing 1 06-21-2011 10:57 AM
Yet another sump pump / pit question SeanFlynn Plumbing 0 01-24-2010 02:07 PM