Sanitary Y Tee Question


Hello All,

I believe using a sanitary tee on the horizontal is against the ontario building code. Does anyone have any experience with this and how I might change it in compliance with code? or at least comment if they believe I might have future problems with this? Maybe leave it?

The farthest is a laundry box and the horizontal sanitary tee is for a laundry tub of which I will add a 45 to come straight out of the wall.

Thanks
Attached Thumbnails
Sanitary Y Tee Question-img_3436.jpg  


Last edited by trophywalleye; 01-11-2013 at 10:59 PM.
trophywalleye is offline   Reply With Quote
Old 01-12-2013, 12:52 AM   #2
moderator
 
TheEplumber's Avatar
 
Join Date: Jul 2010
Location: Idaho
Posts: 6,888
Rewards Points: 56
Default

Sanitary Y Tee Question


I'm confused-
I see a wye on its side. Is that for the sink?
If you were plumbing off the UPC, You could not horizontal wet vent the sink the way you have. But I have no idea how your code reads.
I also see a san t on its back directly downstream from the washer box. That should be a combination wye/45.

__________________
When posting in forums, letting us know your location will help others give better feedback/advice/solutions to your questions
TheEplumber is offline   Reply With Quote
Old 01-12-2013, 07:36 AM   #3
Member
 
Join Date: Jan 2009
Location: WV
Posts: 2,907
Rewards Points: 2
Default

Sanitary Y Tee Question


I don't know exactly why, but having a sanitary tee on its back is a code violation. But there was one installed that way in a house I used to own. It had been that way for more than 50 years, apparently without issue. Can one of the pros here please explain why it's a code violation??
md2lgyk is offline   Reply With Quote
Old 01-12-2013, 07:49 AM   #4
Roofmaster
 
Join Date: Oct 2012
Location: Maryland
Posts: 3,621
Rewards Points: 22
Default

Sanitary Y Tee Question


A Wye and an 1/8 bend, or a long sweep Wye gets the waste water going in the right direction. Those Tees are OK for vents, Not too good for waste.
I dont know when the change came about, but its a good one. I have opened up a lot of clogged up Galvanized Tee's over the years. Water running into the back of those just makes all kind of turbulence, and debris settles to the bottom, I guess. That cleanout should be turned up to a 45 degree angle too, IMO.
__________________
" A lot of men build things, and a lot of things fall down "

jagans is offline   Reply With Quote
Old 01-12-2013, 08:58 AM   #5
Member
 
Join Date: Dec 2010
Posts: 35
Rewards Points: 0
Default

Sanitary Y Tee Question


Sorry for the confusion. The Wye tee on its side is for the laundry tub, not a cleanout. It will have a 45 attached to it so that it comes straight out of the drywall.

Does anyone have any suggestions to make this proper? or do you think I will have any problems with it.

Is there a problem with the sanitary tee vent too?

Last edited by trophywalleye; 01-12-2013 at 09:08 AM.
trophywalleye is offline   Reply With Quote
Old 01-12-2013, 10:27 AM   #6
moderator
 
TheEplumber's Avatar
 
Join Date: Jul 2010
Location: Idaho
Posts: 6,888
Rewards Points: 56
Default

Sanitary Y Tee Question


Quote:
Originally Posted by trophywalleye View Post
Sorry for the confusion. The Wye tee on its side is for the laundry tub, not a cleanout. It will have a 45 attached to it so that it comes straight out of the drywall.

Does anyone have any suggestions to make this proper? or do you think I will have any problems with it.

Is there a problem with the sanitary tee vent too?
You just asked 2 questions that are not going to have concrete answers. These are the kind of questions that plumbers discuss and argue about during break time.
__________________
When posting in forums, letting us know your location will help others give better feedback/advice/solutions to your questions
TheEplumber is offline   Reply With Quote
Old 01-12-2013, 01:28 PM   #7
Newbie
 
Join Date: Nov 2010
Location: Canada
Posts: 10
Rewards Points: 0
Default

Sanitary Y Tee Question


I am starting a laundry room remodel in the basement and have done some reading on the subject - at least to me looks like your venting take off is too low - it needs to be 6" above the highest rim ( or 42" from the floor whichever is larger ) - in this case the top of the stand pipe for the washing machine.

It is hard to see in the picture, but when drilling holes, the max they can be is 60% of the width ( for non-load walls, 40% for load walls ) with a min 5/8 to the edge - check it out and possibly reinforce a bit if below 5/8 if you plan to hang heavy cabinets on the wall.
euroboy is offline   Reply With Quote
Old 01-12-2013, 01:45 PM   #8
moderator
 
TheEplumber's Avatar
 
Join Date: Jul 2010
Location: Idaho
Posts: 6,888
Rewards Points: 56
Default

Sanitary Y Tee Question


I looked at the image once more- I see at least 5 code violations. Some minor- some major
clothes washer requires 2" drain- some areas-3"
sink requires 2" drain and needs a vent
Santee on its back in a drain line
ptrap w/cleanout cannot be concealed
Venting must rise to 6" above the flood rim as previously stated
__________________
When posting in forums, letting us know your location will help others give better feedback/advice/solutions to your questions
TheEplumber is offline   Reply With Quote
Old 01-12-2013, 01:50 PM   #9
Newbie
 
Join Date: Nov 2010
Location: Canada
Posts: 10
Rewards Points: 0
Default

Sanitary Y Tee Question


I forgot to comment on the drain - you would be able to stack vent both drains since you are within the 8' for the 2" and 5' for the 11/2" ( ie no need for the venting pipes). The problem is that the rough-in for the laundry sink is 13" FF - the p-trap for the washing machine needs to be 6 to 18" above the floor - in both cases when connecting to the stack for stack venting a san. t has to be used and only one item per branch.

The setup you have right now is a common vent with the 2" being partly a wet vent for the sink - the sizes are fine and meet the FU requirements, but I hope someone does comment if this is allowed for a washing machine drain in Ontario.

P.S. I took another look at the image and can't tell if that is a 2" pipe - if not my comments don't apply.

Last edited by euroboy; 01-12-2013 at 01:56 PM.
euroboy is offline   Reply With Quote
Old 01-12-2013, 02:29 PM   #10
moderator
 
TheEplumber's Avatar
 
Join Date: Jul 2010
Location: Idaho
Posts: 6,888
Rewards Points: 56
Default

Sanitary Y Tee Question


Quote:
Originally Posted by euroboy View Post
I forgot to comment on the drain - you would be able to stack vent both drains since you are within the 8' for the 2" and 5' for the 11/2" ( ie no need for the venting pipes). The problem is that the rough-in for the laundry sink is 13" FF - the p-trap for the washing machine needs to be 6 to 18" above the floor - in both cases when connecting to the stack for stack venting a san. t has to be used and only one item per branch.

The setup you have right now is a common vent with the 2" being partly a wet vent for the sink - the sizes are fine and meet the FU requirements, but I hope someone does comment if this is allowed for a washing machine drain in Ontario.

P.S. I took another look at the image and can't tell if that is a 2" pipe - if not my comments don't apply.
This just goes to show the differences between codes. Most of what you said will not pass UPC- no idea of OP's AHJ
Also, look at the washer box- appears to have a 2x1.5 bushing

__________________
When posting in forums, letting us know your location will help others give better feedback/advice/solutions to your questions
TheEplumber is offline   Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
3 Phase meter socket question a320200 Electrical 4 12-11-2009 12:45 AM
An unasked question is the only dumb question jackie treehorn Kitchen & Bath Remodeling 1 09-20-2009 08:24 PM
A question about water preassure. reasonforseason Plumbing 5 04-14-2009 04:36 PM
Wye vs. Sanitary tees gsgtree Plumbing 2 11-26-2008 09:46 PM
Basement Renovation Question KUIPORNG Remodeling 234 08-26-2008 08:19 AM




Top of Page | View New Posts

Copyright © 2003-2014 Escalate Media. All Rights Reserved.