#1 |
San-T for Vent
Is it permissible to use a San-T like I have in the picture. It is going vertically to a Vent only--not a drain.
To the left is the washer trap. The right is towards the sewer. Thanks for any help! |
#2 |
San-T for Vent
it is where i live
be careful my advice only comes from general knowledge i know about the 4 rules it takes to plumb and they are 1 poop needs to flow down hill. 2 hot on left cold on right 3 i get a pay check on Mondays 4 do not chew finger nails at or after work. |
#3 |
San-T for Vent
the tee is correct for airflow
#4 |
San-T for Vent
Thanks for the confirmation! Everything is flowing as it should be so far.
#5 |
San-T for Vent
You must use drainage fittings below the flood level of the fixture. A wye and eight bend should be used instead. But no one will probably notice the tee.
#6 |
Thread killer
San-T for Vent
Not required in my area. Must be different in yours?
You can have it good, fast or cheap. Pick two. |
#7 |
call me E
San-T for Vent
Agreed, as long as it's not more then 45* from the vertical
When posting in forums, letting us know your location will help others give better feedback/advice/solutions to your questions |
#8 |
San-T for Vent
uniform plumbing code 905.2 Vents less than six inches above the flood level of the rim of the fixture SHALL be installed with approved DRAINAGE fittings, material and grade to the drain.
Thanks |
#9 | |
call me E
San-T for VentQuote:
But I will say that a combo is the preferred method. However. if santees are not allowed, i've got 20+ years worth of rough-ins in multiple states to change. Besides, who said he works under the UPC? BTW, I still plumb under a revised 2003 UPC, but I understand Idaho is/has adopted it's own code. So, more battles with the AHJ
#10 |
Thread killer
San-T for Vent
I'm in Canada. I've noticed our plumbing codes can be a little more permissive than yours. From what I can see in ours, there is no difference for vent fittings regardless of the proximity to the flood rim. That fitting would be permitted where I am, in its present location. I will admit that its easier to find code references from the U.S. and have gotten happy smiles from inspectors when I used them here.(They were pleased to see someone went above code, I guess)
#11 | |
Doing it myself
That even seems kind of vague, actually The section i have that discusses what YOU'RE talking about is 905.3 Unless prohibited by structural conditions, each vent shall rise vertically to a point not less than 6 inches above the flood level rim of the fixture being served before offsetting horizontally, and where two or more vent pipes converge, each such vent pipe shall rise to a point at least 6 inches above the flood level rim of the plumbing fixture it serves before being connected to any other vent. Vents less than 6 inches above the flood level rim shall be installed with approved drainage fittings, material and grade to the drain. The whole section is talking about where vents travel horizontally to connect to one another.... Anyway, code is open somewhat to interpretation.....
Journeyman Plumber |
| The Following User Says Thank You to Alan For This Useful Post: | TheEplumber (08-13-2012) |
#12 |
San-T for Vent
I have seen a plumber inspection make people tear out fittings that weren't drainage below the flood level as mentioned. Just thought I would give a heads up. Some inspectors don't know or care. But that is the code.
Thanks |
#13 |
Master Plumber
San-T for Vent
will it work yes, up to code no. at least under The IPC.
Experience is Knowing what to do next, Skill is knowing how to do it To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. |
| Display Modes | |