Bubski27 04-27-2013 02:32 PM
Hey all I have a natural gas hookup on the patio. Was wondering if there was some kind of quick connect splitter I could hook up so i can have my gas firepit and BBQ going at the same time
oh'mike 04-27-2013 08:50 PM
I moved this to plumbing for you---
You need to post a picture of what you have----typicality a T- is used and two seperate quick connections are used----
The real question is this---will that pipe supply enough gas to run both units at the same time---
Get the BTU ratings from both and the pipe size and come back---
ben's plumbing 04-27-2013 09:25 PM
you go mikey.....:thumbup::thumbup::thumbup:ben sr
hammerlane 04-28-2013 08:50 AM
1 Attachment(s)
My guess is 45K BTU grill and 80K BTU firepit on a 1/2 line. Thats a total of 125K BTU
This table is in the Natl Fuel Gas Code. 10 feet of 1/2 black pipe can deliver 131 cubic feet of gas per hour. So thats about 132K BTU per hour. Since 1 cub foot of natural gas is equal to 1015 BTU.
So hopefully your run of 1/2 is less than 10 feet to have both function properly if going at the same time.
If you do need to use a Tee to split anything, note that a Tee is equivalent to 3.10 feet of straight pipe.