Old 10-07-2012, 03:53 PM   #1
pressure relief valve broken ?
I can "fix" my low water pressure by screwing in the set screw on my pressure relief valve. Does that mean its broken ?
davisdave is offline   Reply With Quote
Old 10-07-2012, 04:29 PM   #2
Most likly, got a picture of it?
Not much to them, most can be rebuilt.
davisdave (10-07-2012)
Old 10-07-2012, 04:37 PM   #3
Old 10-07-2012, 04:56 PM   #4
It's a Watts N35B size 1mobel u, std 50 range 25-75 see attached image
Old 10-07-2012, 05:06 PM   #5
http://media.wattswater.com/1915088.pdf
Old 10-07-2012, 05:19 PM   #6
thanks for the diagram
What I had done is "turn the adjusting bolt clockwise
to increase pressure" This allowed the water pressure to return to "normal". Was my need to do this an indication of a bad valve or a lower city pressure?
Adjustment
Regulator is factory preset to 50psi. (346 kPa) To adjust pressure
setting, loosen the lock nut and turn the adjusting bolt clockwise
to increase pressure, counterclockwise to decrease pressure.
Caution:
Any time a reducing valve is adjusted, the use of a pressure
gauge is recommended to verify correct pressure setting.
Old 10-07-2012, 05:22 PM   #7
http://www.youtube.com/watch?v=eDxx_od_LL0
That doesn't indicate it is broken but does indicate it is working as designed in most instances, although they can often function fairly normal with a broken spring. When adjusting, I was taught to make the final adjustment on the increase.
For future reference, you have a pressure regulating valve. Pressure relief valves are constructed different and serve a different purpose.
Good luck with increasing your pressure.
Fairview is offline   Reply With Quote
Pressure Relief Valve Leaking new_DIY Plumbing 10 10-04-2012 11:24 PM
pressure relief valve at water shutoff swkinv Plumbing 4 05-23-2012 10:35 PM
leaking pressure relief valve on heating water boiler benjamintr HVAC 13 01-29-2011 06:32 AM
Boiler pressure relief valve leaking Jaschance HVAC 3 02-08-2010 11:05 PM
Water Heater Pressure relief valve problem joedadog Plumbing 5 01-14-2009 02:58 PM