Currently I have two sinks from two adjoining bathrooms connecting to a 1 1/2" vertical drain. I would like to replace the vanity in one of the bathrooms with one having a double sink. This would mean three fixtures would be connected. The double sink would be plumbed so each one would have its own p-trap and connect to a double fixture cross.
I called a local plumbing company and they said they would plumb the new fixtures but that it wouldn't be to code. They said it would be fine having three fixtures just not to code??
What would be the consequences of having three fixtures tied together. Is it just to protect the possible situation where are three fixtures are being used or draining at the same time?
joecaption 12-20-2012 10:24 AM
My guess is without the 2" line that should be there it my suck the water out of the trap as it was draining.
tylernt 12-20-2012 10:51 AM
Lav sink is 1 DFU (Drain Fixture Unit):
http://www.engineeringtoolbox.com/dr...es-d_1077.html
Looks like 1 1/2" pipe can support up to 3 DFU:
http://www.engineeringtoolbox.com/fi...es-d_1104.html
So on the face of it, 3 bathroom sinks on a 1 1/2" drain might indeed be legal. However there may be other restrictions that apply that are in the text of the code, but not mentioned in the above table... so it's not a slam-dunk. Plus you're in Canada, dunno what is code up there.
TheEplumber 12-20-2012 12:30 PM
199 Attachment(s)
Local codes play a part in how many DFU's a pipe will handle. Vertical pipes generally allow more then horizontal too.
I would not put 3 lavs on a 1.5" pipe.
And I would not use a sanitary cross- another code violation- at least for me
Alan 12-20-2012 09:11 PM
To further add to the code ruling on this issue (UPC Based response) :
704.2 Two fixtures set back to back or side by side within gthe distance allowed between a trap and it's vent may be served by a single vertical drainage pipe provided that each fixture wastes separately into an approved double fixture fitting having inlet openings at the same level.
706.2 ..... No fitting having more than one inlet at the same level shall be used unless such fitting is constructed so that the discharge from one inlet cannot readily enter any other inlet. Double sanitary tees may be used when the barrel of the fitting is at least two pipe sizes larger than the largest inlet.........
Also agree with above comments about 1-1/2" drain being too much for 3 lavatories.
RalphPeters 12-21-2012 12:43 AM
I appreciate the replies.
What would be the consequences of an overloaded drain?
Javiles 12-21-2012 08:01 AM
slow draining when multiple sinks in use. ger gulling, possible trap siphon. look don't knock yourself out use the correct combination on the drains you'll be alright. unless its inspected work.
RalphPeters 12-21-2012 10:26 AM
2 Attachment(s)
So would I want the double fixture fitting above the t fitting? I can only find the double in a 2 x 1 1/2 x 1 1/2 x 1 1/2 so a reducing bushing would be necessary?
Javiles 12-21-2012 01:55 PM
1 1/2 double sanitary tee. they make m... on the top use a 1 1/2 (street) sanitary tee. slips into the hub. 2 inch will take up to much space between the arms. be careful that fitting in the picture is a combo not a sanitary
ben's plumbing 12-21-2012 06:45 PM
1 1/2 would be to small...consequences would be its done wrong so it will drain slow ....Iam sure you don't want that because you came to this site for the answer....you now have it....good luck ben sr
Javiles 12-21-2012 11:38 PM
Agreed but that's what he has in the wall on the vertical 1 1/2 :whistling2: