New Water Heater Woes - Plumbing - DIY Home Improvement | DIYChatroom
Old 02-22-2013, 10:45 AM   #1
Household Handyman
Rewards Points: 1,408
new water heater woes
Not sure whether this would be electrical or plumbing so I posted in general.
Got a call to a lady's home with complaint of no hot water. The unit was outside, not covered, and looked like a disasater waiting to happen. I could find nothing wrong with this unit. There was power to both legs of the unit and the ground was tied in correctly.
With the power off and the elements disconnected I had 12.3 Ohms on each element, that should show a good element or so I was taught years ago.
The thermostat tested correctly with the VOhM meter also. Power restored to the elements and all testing shows power to the elements and power going through each element. But still no hot/warm water.
The homeowner tells me that she has talked to a plumber about installing a new unit but the plumber does not wire in water heaters. So I go out to wire in the new unit. First--make sure the tank is full, it is.
Second--check to make sure I have the wiring correct, and I did. Once the unit is wired up and power is on it, everything checks out O.K. The new elements were checked again and all seems well. One strange thing is that I do not hear the noise normally associated with a unit starting up, that sort of "frying" sound from within the tank.
With these newer tanks I'm not sure I will hear this. After thirty minutes or so there is no warm water. This morning she calls to tell me that there is still no warm/hot water from the new unit.
This is not my first water heater wiring but certainly the most puzzling. I'm thinking I'll kill the power to the tank, drain the tank, and inspect the new elements just to be sure. Please--any other ideas? Thanks, David
Old 02-22-2013, 12:17 PM   #2
Originally Posted by Thurman View Post
Not sure whether this would be electrical or plumbing so I posted in general. Got a call to a lady's home with complaint of no hot water. The unit was outside, not covered, and looked like a disasater waiting to happen. I could find nothing wrong with this unit. There was power to both legs of the unit and the ground was tied in correctly. With the power off and the elements disconnected I had 12.3 Ohms on each element, that should show a good element or so I was taught years ago. The thermostat tested correctly with the VOhM meter also. Power restored to the elements and all testing shows power to the elements and power going through each element. But still no hot/warm water. The homeowner tells me that she has talked to a plumber about installing a new unit but the plumber does not wire in water heaters. So I go out to wire in the new unit. First--make sure the tank is full, it is. Second--check to make sure I have the wiring correct, and I did. Once the unit is wired up and power is on it, everything checks out O.K. The new elements were checked again and all seems well. One strang thing is that I do not hear the noise normally associated with a unit starting up, that sort of "frying" sound from within the tank. With these newer tanks I'm not sure I will hear this. After thirty minutes or so there is no warm water. This morning she calls to tell me that there is still no warm/hot water from the new unit. This is not my first water heater wiring but certainly the most puzzling. I'm thinking I'll kill the power to the tank, drain the tank, and inspect the new elements just to be sure. Please--any other ideas? Thanks, David
. Power to both legs, or power ACROSS the legs? Sounds like you may be seeing 120 but no 240.
64pvolvo1800 is offline   Reply With Quote
Old 02-22-2013, 12:20 PM   #3
Rewards Points: 12,830
Have you tryed opening up the drain to see if hot water comes out?
Does any water come out of the faucets, or does it come out and it's just not hot?
Be sure the power is shut off at the circuit breakers. Disconnect one of the two wires from the heating element. Now using an ohm meter measure the resistance between the two terminals.
If the heating elements are good then you will get a reading of less than 50 ohms. If the heating element is burned out the meter will read infinity, or open circuit.
The meter should also give you an open circuit reading between the terminals and the metal housing of the water heater element.
Old 02-22-2013, 03:02 PM   #4
Household Handyman
@ "64pvolvo1800" : Power to each leg is 120vAC as tested against the ground wire. Yes, testing across both legs gives me 220vAC. This is at the connection to the unit, and at the top of the thermostat. Each leg at the element is 120vAC as tested to each screw and the tank, both screws are 220vAC on each element.
joecaption" : Yes I have checked the bottom drain after 30 minutes and it is cold water. Yes water comes out of both faucets at the kitchen sink, hot water side is cold, and cold is cold. Each of the new elements were tested for Ohms with both wires disconnected from the elements. Both elements tested at 12.8 Ohms. Each element was tested by using each screw and testing to the tank for a short--not a short. My next thing to do is to find my darn lost Ohm meter (clamp meter) and test for current draw on the wiring. Thanks for the ideas, David
Old 02-22-2013, 03:22 PM   #5
I suggest your post be moved to plumbing so do not give up yet. Later today when people come home from work someone may come up with an idea.
Old 02-22-2013, 03:39 PM   #6
Biarski's Avatar
I'd be surprised if it were plumbing related, since the water is flowing, but I'm no plumber. I would suggest test for voltage at the elements when the thermostat goes from "off" to 130 or whatever you set it at. You should see it go from 0 to 220 and back as the thermostat calls for heat. With a new tank I'm not surprised that everything checks out. Since the problem didn't change from the old to the new, the problem likely exists in the incoming wiring. The most frustrating part is that it's not really all that complicated. Not sure what else to check not being there... please post your findings
Biarski is offline   Reply With Quote
Old 02-22-2013, 03:53 PM   #7
Well in review, watts = heat, watts = volts x amps, amps = 220/12 or about 20,
So 220v * 20a = ~4400w x 2 elements is 8800watts of power that's going somewhere! So yeah, grab your clamp and check it out. If you have voltage on the elements and resistance meeting voltage, then power should be consumed and turned to heat. I suspect a faulty breaker that is passing no current.
Did you have the thermostat calling for heat when you checked voltage on the elements?
Old 02-22-2013, 07:48 PM   #8
Household Handyman
"64pvolvo1800"---You're pretty close with your call. The old, and new, elements are 4500 watts each and they are tied to a 30 amp dual breaker to get the 220vAC. It's raining as if Noah is coming soon here now so tomorrow morning will be the amp draw test. One thing I keep going back to is the fact that they have had hot water for over a year with the old unit and then "poof", the hot (or even warm water) suddenly stopped. I think I failed to mention that I pulled the elements from the old unit after it was replaced for inspection and could barely pull the bottom element out due to the calcium/lime build-up on it. That's very common around here though. The top element had some coating but not too bad.
Old 02-22-2013, 09:29 PM   #9
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,034
Are you measuring 240 across the element? Or 120 from each element terminal to ground?
Coastal South Carolina
Old 02-23-2013, 08:13 AM   #10
New heater is same as old, you would think there is a weakness in the breaker. It tests with the meter but when the call is made for power the breaker craps out. What does a new breaker cost? Are those dual breakers a known problem. I spent a few years working on very complicated jaguars, many times the performance problems were so simple you could not believe you missed it.
paintdrying is offline   Reply With Quote
Old 02-23-2013, 08:46 AM   #11
Master Plumber
Javiles's Avatar
Rewards Points: 984
i see this all the time from pro plumbers and electricians..
Experience is Knowing what to do next, Skill is knowing how to do it
http://www.americandrain.net
Javiles is offline   Reply With Quote
Old 02-23-2013, 11:46 PM   #12
Biarski's Avatar
The breaker might be bad and it could still read 220v, but then it ought to also trip under load... It's probably only about $10 or so depending on the brand.
Old 02-24-2013, 06:48 AM   #13
A "Handy Husband"
rjniles's Avatar
If you are reading 240 across the heating element, the breaker is not bad.
Old 02-24-2013, 07:37 AM   #14
Rewards Points: 1,214
Any hot water from the TP when flipped? Hot water piped correctly and not cut off or valved off somewhere? Did the customer tell you everything ? Like what the people did before you. Thermostat opening to soon or acting up. I'd be real suspicious of that thermostat/limit even though the readings were good.
No Warranty Means- If it breaks in half you get to keep both halves.
COLDIRON is offline   Reply With Quote
Old 02-24-2013, 08:22 AM   #15
Just for kicks and giggles, take the old elements and run 220 to each and plug in briefly. See it they each heat up. That will confirm that the problem is electrical and not plumbing. You have to be losing the 220 TO the element or else they HaVE to heat. Physics
The Following User Says Thank You to 64pvolvo1800 For This Useful Post:
COLDIRON (02-24-2013)
water heater drip kdange1 Plumbing 6 10-29-2014 06:26 PM
How to properly drain and flush a hot water heater? speedster1 Plumbing 9 04-17-2012 10:55 PM
Gas Water Heater, water not hot enough - Thermostat or Sediment makunag Plumbing 15 08-28-2010 12:00 AM
