Is This Legal - Plumbing - DIY Home Improvement | DIYChatroom
Old 04-07-2014, 06:59 PM   #16
Plumber
TheEplumber's Avatar
Rewards Points: 904
Originally Posted by Robpo View Post
E,
Would that be at the toilet end or before the septic end where it leaves the house? When I built my home he wanted it where it left the house.
Thanks,
It's actually required at the upper end and where it exits the house. But we used to be allowed to use a toilet as a clean out- this may still apply for you. He'll let you know, the fix is easy.
You may have to change the horizontal to vertical 90 to a combination y &45- off the end of the y would be the toilet, the vertical 3" riser/vent would become the clean out. After the CO it can be reduced back to a 2" vent
The Following User Says Thank You to TheEplumber For This Useful Post:
ben's plumbing (04-07-2014)
Old 04-08-2014, 08:57 AM   #17
Rob
Robpo's Avatar
Rewards Points: 826
Originally Posted by MTN REMODEL LLC View Post
Find any gold when you're digging out there.......
Not yet. If you want to come over and help dig footings you can keep all you find. Bring a jackhammer it's all rock.
Robpo is offline   Reply With Quote
Old 04-08-2014, 09:14 AM   #18
Remodel and New Build GC
MTN REMODEL LLC's Avatar
Rewards Points: 3,784
I was just there... traveling from SF to Co... with my daughter and her lab.. Cooper.
Took Cooper right into the Casino with us and played.... a new first for me... taking your dog right into the Casino....
You have a nice small town friendly feel out there .... in the middle of ??.
Best and Good luck with the build.
PS: Coop did not like the big stuffed bear in the corner.
MTN REMODEL LLC is offline   Reply With Quote
Old 04-08-2014, 05:17 PM   #19
Rewards Points: 2,104
Originally Posted by ben's plumbing View Post
that would be clasified as a wet vent...vent should be above the flow line..some areas allow for wet venting..but imo its not a good vent system.. if you can rip it out and redo it with vent off top..
Ben a dry flat vent is not very wet....
The Following User Says Thank You to Ghostmaker For This Useful Post:
MTN REMODEL LLC (04-08-2014)
Old 04-08-2014, 05:43 PM   #20
Rob
Robpo's Avatar
Rewards Points: 826
This is how I did it the first time.
Old 04-08-2014, 06:56 PM   #21
Rewards Points: 582
anytime water is above the vent we always called it a wet vent because at one point water is in the vent stream.... is that in the book ipc or upc ?????
Old 04-08-2014, 09:21 PM   #22
ipc.......
The Following User Says Thank You to MTN REMODEL LLC For This Useful Post:
ben's plumbing (04-08-2014)
Old 04-09-2014, 05:49 PM   #23
Under the IPC ben Only Bathroom group fixtures are allowed to be wet vented. Bathroom group defined as A toilet, 1 lav, 1 shower or a tub, A bidet and a emergency floor drain in the bath room. You can have up to 2 bathroom groups vented on a single wet vent. But there are things to be aware off. All lavs must be vented regardless. The theory is if you use a lav as a wet vent and that wet vent gets blocked you will notice your sink no longer drains. So you call Javiles out and he snakes it and reopens your vent.
A dry flat vent having nothing draining through it can block your vent is lost and your not the wiser...
The wet vent is also based on using oversized pipe. 1.5 inch 1 DFU, 2 inch 4 DFU, 3 inch 10 DFU = 2 Bathroom groups.
Under the IPC 1.25 inch pipe still is in the code.
You have two types of wet vents one being horizontal the other being vertical. The key with vertical is the toilet must always connect below the other fixtures.
It was a struggle for me when this stuff was brought into the state. Being our old code was everything was vented regardless in a vertical way...
Old 04-09-2014, 06:06 PM   #24
Rewards Points: 582
ok ...in the op question he ask if its code....i said we called that a wet vent because water passes the vent opening....which i said some places allow for wet venting...which i said i don't like wet venting at all because i don't think it the best system for venting... and you said a dry vent is not very wet.... I know what the ipc,upc code says about venting.. in the op picture is it legal to vent that way...
Old 04-09-2014, 06:37 PM   #25
Plumber
Rewards Points: 904
IMO- the picture was wrong because the vent was not taken off above the trap's crown.
I can run horizontal flat vents below the flood rim- when there is no other way do to structural conditions
ben's plumbing (04-09-2014)
Old 04-09-2014, 08:22 PM   #26
No because he has a dry flat vent no fixture attached to it IPC does not allow a dry flat vent in any circumstance. A fixture vent must rise 6 inches above the flood level rim prior to turning horizontal. As another poster noted the trap cannot be higher then its vent.
The Following 2 Users Say Thank You to Ghostmaker For This Useful Post:
ben's plumbing (04-10-2014), MTN REMODEL LLC (04-09-2014)
Old 04-09-2014, 09:18 PM   #27
Honest E.... I'm sure no code guy, or even a plumber, but what code cite allows that..... I do understand a BO might allow/overlook it.
Old 04-09-2014, 09:35 PM   #28
Plumber
Rewards Points: 904
upc 905.3
Old 04-09-2014, 09:52 PM   #29
upc 905.3
You are darn tootin dead on correct..... Thank You for the education
Any idea if IPC allows that also.?(Don't look it up.... your word is good by me
Edit PS: (Actually that makes good sense, especially with the consideration you use all drainage fittings on it)
Old 04-09-2014, 10:02 PM   #30
Plumber
Rewards Points: 904
Threads getting hijacked but you might like this read http://www.plumbingengineer.com/feb_11/designers.php