CHRIS650 12-11-2010 02:02 AM
i have a slow leak coming out of the pressure valve and was wondering if i have to change it or if there is another solution for the leak.
majakdragon 12-11-2010 07:33 AM
For about $15, you can replace it and feel safer. Either the spring is weakening or the valve opened and something got stuck under the seat. You could use the handle on the end of the valve to quickly open and shut the valve to see if it is a piece of debris holding the gate open. Be careful when doing this since you are dealing with hot water.
Work4living 12-11-2010 08:07 AM
Chris,
Do you have a small blue tank attached to the cold supply of the waterheater? Also you should check your water pressure. It is possible that the spring is weak. Also very likely it is the result of failure of the expansion tank or too much water pressure.
COLDIRON 12-11-2010 08:20 AM
Check your auto fill valve it might be stuck open continuously feeding boiler. Check pressure temp gage on front of the boiler if its near 30# it's to high. Should be around 12#
Work4living 12-11-2010 08:22 AM
Cold this is a domestic water heater not a boiler.
COLDIRON 12-11-2010 08:36 AM
Thanks Work I didn't see it mentioned any where. New glasses are in order.
burnt03 12-11-2010 09:40 AM
Check your PRV. Maybe it failed and the T&P is just doing it's job?