-   -   How to vent though church roof (http://www.diychatroom.com/f7/how-vent-though-church-roof-169628/)
Ron S. 01-20-2013 01:26 PM
Knowing there’s only one hole in the church roof to use for a vent, and that I have approximately fifty feet of horizontal vent and approximately one hundred feet of vertical vent, how can I satisfy an inspector, while knowing "no more than one third of a minimum sized vent can be installed horizontally?" I'm thinking over size the vent piping, but by what percent? Appreciate any suggestion. thanks!
Ron S.
TheEplumber 01-20-2013 01:38 PM
199 Attachment(s)
Ron S.
From the fixture being served- Upsize the vent one pipe size diameter- UPC
jagans 01-20-2013 02:51 PM
Why not just put another hole in the roof. It will be more Holy. Its a church after all. :thumbsup:
Alan 01-20-2013 03:16 PM
LOL'ed.
Agree with Eplumber.
Upsizing the vent from the fixture being served eliminates the ruling on length.
That said, you CAN upsize the line at the end of it's maximum distance, but doing so will limit the second run of piping.
For example, if you run 1-1/2" vent to it's max distance, upsize to 2" pipe, you are then limited to the maximum lengths of a 2" vent. If your fixture requires a 1-1/2" vent, and you run 2" from the fixture, there are no max distance limits.
Ron S. 01-21-2013 01:34 AM
Re; How to vent chruch roof
I should of mentioned there are two bathrooms and a small kichen to be vented (seventeen fixture units). The reason for running one vent though an existing space in the roof is because the church has been declared a historial land mark and there are religious paintings on all the four walls. Thanks to Eplumber and Alan for the help.
Ron S.
Alan 01-21-2013 09:41 AM
17 fixture units = 2"
2" max distance is 120'
1/3 of that is 40'
You say roughly 50 feet....is it 50 + or 50 - ?
If you can run any portion of that on a 45* angle before going horizontal, that is still considered vertical. Depending on how much room you have, you may still be able to get a 2" pipe to work without upsizing.
TheEplumber 01-21-2013 09:47 AM
199 Attachment(s)
1/3 of that is 40'
Don't forget the rule about cross sectional area of the bldg. drain. I'd run it in 3"
Alan 01-21-2013 09:43 PM
True, but i'm assuming they're tying in to an existing vent. You may be right. :thumbsup: