Old 12-18-2010, 04:32 PM   #1
Gas water heater problem
I have a 48 gal. Bradford White gas water heater that is @ 10 yrs old. The inducer motor comes on, the burner lights and the motor continues to run momentarily after the burner goes out. About every other cycle, the 15A breaker trips during the middle of the cycle. Any ideas? Thanks for any help.
RapidRobert is offline   Reply With Quote
Old 12-18-2010, 04:51 PM   #2
the Musigician
DangerMouse's Avatar
It trips when the motor is NOT running?
DM
[SIGPIC][/SIGPIC]Click
to see some of my original magic tricks and trick boxes!
Old 12-18-2010, 05:52 PM   #3
No, it trips once the motor starts. The motor and the burner are both running.
Old 12-18-2010, 06:02 PM   #4
the Musigician
I'd check the wiring. Look for loose connection.
DM
Old 12-18-2010, 06:06 PM   #5
I checked the motor and the wiring inside the panel and everything looks good and tight. Even replaced the breaker at the fuse box. Anyone know how to test the motor, and control unit?
Old 12-18-2010, 06:07 PM   #6
Is the induction motor getting hot......If so you are losing it, and your next move is a new heater.....replacement motor is quite pricey.
Work4living is offline   Reply With Quote
The Following User Says Thank You to Work4living For This Useful Post:
RapidRobert (12-18-2010)
Old 12-18-2010, 06:11 PM   #7
the Musigician
True, they want an arm and a leg for those things.
A +10 YO heater might just be telling you it's time for a new one. Po)
DM
The Following User Says Thank You to DangerMouse For This Useful Post:
Work4living (12-18-2010)
Old 12-18-2010, 06:14 PM   #8
Just checke the motor--it doesn't feel hot at all. Did find a blue wire (runs from the control unit to the ignitor/sensor) that looks like it may have arced against the panel cover.
Old 12-18-2010, 06:20 PM   #9
the Musigician
Hmm, that's probably not a good thing.... huh?
Wrap some black tape on it and see if it stops?
DM
Old 12-21-2010, 08:12 AM   #10
Checked with Bradford White tech support. They tell me that the only components capable of tripping the breaker are the inducer motor and the 120/24v transformer. Got the transformer and and motor pressure switch ordered. Guess I'll be changing them out on Wed. Motor assy itself is not too badly priced (under $200), but I'll save that as a final option since the transformer and switch are under $40 together.
Water heater sitting idle - problem? 2muttsmom Plumbing 5 08-08-2010 02:30 PM
Water Heater Problem mdong HVAC 19 11-29-2009 11:53 AM
Bosch 1600H Tankless Water Heater natemclain HVAC 13 08-24-2009 11:33 AM
Water heater problem bear1957 Plumbing 23 11-01-2007 04:53 PM
Draining a hot water heater singforsupper Plumbing 1 06-07-2006 07:01 PM