markharmon 04-28-2013 03:20 PM
basement shower
I have a single story house and if I wanted to add a shower in my basement obviously I would run the trap and drain line into the main sewer line under the slab but to vent it I would have to run a vent line up and over the first floor fixtures, correct? Otherwise I would be wet venting between floors, which is not allowed.
TheEplumber 04-28-2013 03:26 PM
199 Attachment(s)
If there are other vents in the basement, you can connect to them as long as you're 6" above the flood rim- usually 42" above the floor.
A shower will require a 1.5" vent.
markharmon 04-28-2013 03:47 PM
If I connect a vent in the basement then the shower would be wet vented by the first floor fixtures, correct?
TheEplumber 04-28-2013 03:59 PM
199 Attachment(s)
Only if you connect it to a waste stack. Do you have other fixtures in the basement? How are they vented?
markharmon 04-28-2013 04:16 PM
yes a toilet and laundry tub both just run into the main waste stack. I have fixtures on the first floor though obviously. if I added a shower in the basement wouldn't i have re-vent it up and over the first floor?
TheEplumber 04-28-2013 04:27 PM
199 Attachment(s)
Since the other basement fixtures are not vented, then I see 2 options- vent as you suggest, or add a mech vent (AAV) on the shower.
AAV's need to be accessible at all times.
markharmon 04-28-2013 04:47 PM
So, either revent up and over first floor or AAV? Now if my basement toilet and laundry tub were vented your saying I could tie into one of those branch vents serving one of those two fixtures?
ben's plumbing 04-28-2013 05:06 PM
yes as long as its above the flood rim..42" above floor..ben sr
markharmon 04-28-2013 05:21 PM
Assuming the basement fixtures were vented and I went this route wouldn't the first floor fixtures still be wet venting the shower since its in the basement?
markharmon 04-28-2013 05:37 PM
Another quick question. The floor rim level. Is that where the trap waste arm is or the actual sink rim itself? I get confused by that.
ben's plumbing 04-28-2013 05:47 PM
not if the basement fixtures were vented from basement through roof by themselves...
TheEplumber 04-28-2013 05:50 PM
199 Attachment(s)
Here is a method of venting a bath room group. It does not matter if it's in the basement or the 5th floor. All the fixtures in this case are vented to one common vent stack.
This common vent rises up through the floor and can then connect to another vent 6" above the flood rim of the fixture served on the upper floor- in this case it's the lav's rim
markharmon 04-28-2013 06:49 PM
If they were just ran as a vent stack and then tied into the main stack vent then I could just run the new shower vent line up and tie into the vent stack serving the basement fixtures?
markharmon 04-28-2013 06:57 PM
So in the picture that is basically a secondary vent stack or would it be a waste/vent stack since it says main. Bottom portion being the waste stack. Fixtures below this floor would then need to re-vent up and and over and tie in to this stack 6" above the flood level? Otherwise you would be wet venting the floor below its fixtures. Am I correct?
ben's plumbing 04-28-2013 07:56 PM
yes...