-   -   basement bathroom venting (http://www.diychatroom.com/f7/basement-bathroom-venting-155910/)
marketbridge 09-05-2012 09:19 AM
I was hoping someone could sketch on this photo where they suggest I put vents for this basement bathroom.
i'm not sure if i can get away with one vent, and if so where,
or if I need a vent for each appliance (shower, wc, lav).
thx
https://dl.dropbox.com/u/79088836/pl...2012_00000.pdf
https://dl.dropbox.com/u/79088836/pl...2012_00000.jpg
DannyT 09-05-2012 10:30 AM
if you run a vent up at the lav you will also need one on the drain for
the shower(between the 4 inch and the 2 inch p-trap).
where do you plan to run the vents to?
you can run 3 inch instead of 4 inch.
it looks like there isn't really isn't enough room for everything in this space.
you need a minimum of 900 sq in in a shower(30x30), and that's on the inside.
marketbridge 09-05-2012 10:40 AM
thx. i am venting up to the roof after tying vents together at basement ceiling.
based on the order of the fixtures, if i only put a vent on the lav and the shower, won't the toilet pull the waste out of the p-trap for the sink when flushing and hence allow gases to travel up the sink drain?
TheEplumber 09-05-2012 11:50 AM
199 Attachment(s)
Your lav will be vented- so no
Are you really planning on putting a tee on it's back for the wc? :no:
marketbridge 09-05-2012 01:47 PM
does this look OK?
https://dl.dropbox.com/u/79088836/pl...2012_00001.jpg