-   -   AAV under island sink (http://www.diychatroom.com/f7/aav-under-island-sink-165472/)
benleef 12-03-2012 12:10 PM
1 Attachment(s)
My in-laws have an island sink. It drains slowly, I believe an AAV under the sink will help greatly. The issue is, the vertical pipe from the basement comes up and then a 90 turn to horizontal run of about 12" then another 90 turn and a horizontal run for 8" and then the trap.
The only easy place to put a T to an AAV would be after the second ninety, right before the trap---would this be OK?
hammerlane 12-03-2012 12:44 PM
Did you take the trap apart and see if there was any clogs?
You cannot use an AAV horizontal. Needs to be vertical or I think no more than 15 degrees from the vertical.
benleef 12-03-2012 01:28 PM
There are no clogs.
The T would be vertical not horizontal. Is it OK if it is vertical after a horizontal run, as long as it is before the trap?
Thanks!
TheEplumber 12-03-2012 04:37 PM
199 Attachment(s)
Originally Posted by benleef (Post 1065524)
There are no clogs.
Thanks!
Best place for it is at the vertical to horizontal 90. If you can't replace that 90 with a tee- AAV on top then any place after that and before the trap will have to do
benleef 12-03-2012 05:12 PM
That is what I figured. Thanks!