Thermostat Issue - General DIY Discussions - Page 2 - DIY Chatroom Home Improvement Forum
Old 01-26-2011, 06:08 PM   #16
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,192
Originally Posted by Ron6519 View Post
This thermostat is a dual voltage unit. It has a switch to change from 110 to 220.
Was the switch placed on the correct voltage?
Ron
Ron
I looked at the installation/ user manual for this t-stat, there is no voltage selector switch.
Dconklin80
What is the rating of the baseboard heater that you are connecting to?
Is it greater than 3500 watts?
Coastal South Carolina
Old 01-26-2011, 06:49 PM   #17
240/208v 60hz
Watts is 500/375
Amps 2.1/1.8
Dconklin80 is offline   Reply With Quote
Old 01-27-2011, 07:15 AM   #18
A "Handy Husband"
rjniles's Avatar
I am thing you have a bad heater unit (low resistance)or a short circuit or cross with ground in the wire from the t-stat to the heater. I see a bare ground wire at the heater junction but none in the t-stat box, is there a ground wire? You need a multimeter with a ohms function. With the power off, open the wire nuts on the white wires in the t-sat box and test toward the heater; you should see in the area of 100 to 150 ohms. Also test each individual wire to a known ground, should read infinity. If you get a bad rading there open the connections at the heater junction box and test the heater alone and the wire alone. I am thing that when you turn the breaker on you are drawing high current and burning up your new t-stat. The t-stat is rated at 3500 watts max, which is a little over 14 amps. What size is the breaker, it should be 20 amps if all the wires are 12 ga. or 15 amps if the wires are 14 ga.
Old 01-27-2011, 10:00 AM   #19
Rewards Points: 1,502
To test the heater itself for a short to ground (that can also blow up the thermostat) --- Label all the wire ends and disconnect the heater from the power wires completely. Using a multimeter (or ohmmeter) test for continuity between each of the heater wires and the heater frame. You should get no continuity, essentially infinite resistance in terms of ohms.
(Between the heater wires you should measure less than 100 ohms.)
AllanJ is online now   Reply With Quote
Old 01-27-2011, 01:40 PM   #20
Great thanks for all that. As far as I know there is no ground wire in thr box. I did notice thst too. Ill try all your sugestions. Thank u.
Old 02-08-2011, 05:20 PM   #21
So just an update turns out the heater unit was bad. Once I got the replaced it stoppes blowing tstats. Thanks for the help.
Furance & AC Issue Lobley HVAC 6 09-12-2009 10:30 PM
Replacing thermostat...................... sktn77a HVAC 6 09-02-2009 10:07 PM
ac/furnace runs whatever thermostat settign donbohn HVAC 1 06-20-2009 05:42 AM
New Thermostat issues when cooling guimond777 HVAC 2 05-04-2009 10:46 AM
Oil Furnace - Swapping out to Programmable Thermostat slappy HVAC 2 12-05-2007 03:57 PM