that is typical with the 2 wires out to the condenser so that says the tranformer is in the air handler furnace section.some thing is going on with your stat or the relay for the fan to run hi speed for cooling.pull the stat off the wall(remove it gently ...sorry
now your faced with the subbase...with the power up on the furnace jump R to G on the subbase you should hear/feel the supply fan run...*then to verify the outdoor section (condenser) jump R to Y for a 5-10 second,and have another pair of eyes out the window to yell out the fan came on on the top of the condenser from your jump.that 2 blue within the condenser tells you can connect the red/white either blue doesn't matter.the running of the condenser has nothing to do with the indoor fan running with this jumping at the base it is totally for testing the 24V out/down to each one.*if you have a meter and can read 24V disconnect the 2 blues,and put your leads out at the condenser on the red and white coming from the house...when you jump R to Y you should see 24V on the meter.(* 2 ways of testing the wire run out to the condenser)with the stat remounted onto the subbase putting the FAN in the on position it should run..in AUTO the fan will only run if the cooling is calling..even if the SYSTEM is off on the stat the fan still will run when put into the ON position.will check back for your feedback.