I added a 100amp garage breaker box about 15yrs ago off my 200amp main. Everything has been fine but as of today the garage main won't reset. I usually turn off the garage main when not in use. Checked the 100amp breaker at the main and is still active. Turned off the main breaker at source and still tripped at garage when tried.
Is it safe guess to say the garage main has been manually reset so much its finally worn out? Thx Jack
Jack Duren is offline   Reply With Quote
Old 12-06-2014, 09:03 AM   #2
Rewards Points: 6,034
That would be my guess.
Old 12-06-2014, 09:13 AM   #3
Remodel and New Build GC
MTN REMODEL LLC's Avatar
Rewards Points: 3,784
Agree..... That is the likely problem.....
But.... if you can't reset your feed at the sub, you can't know that the breaker at your main is NOT tripping because of no fault... ie... that you do not have a fault downstream of your sub..
Different breakers will not trip simultaneously.
MTN REMODEL LLC is offline   Reply With Quote
Old 12-06-2014, 09:25 AM   #4
Rewards Points: 14,290
Tried shutting off all the breakers in the panel in the garage to see if it will reset?
If it resets then, start turning on the breakers one at a time to find the line with the possible fault.
Really should not be using a breaker as a switch.
The Following 3 Users Say Thank You to joecaption For This Useful Post:
jmon (12-06-2014), MTN REMODEL LLC (12-06-2014), ToolSeeker (12-06-2014)
Old 12-06-2014, 10:29 AM   #5
Idiot Emeritus
Rewards Points: 1,492
If, by this, you mean the 200 was turned off then the 100 was turned on (and stayed on) and when the 200 was turned back on the 100 tripped, then you almost certainly have a fault downstream from the 100.
Breakers are not designed to be used as switches unless they are marked SWD. The only SWD breakers I've seen are 15s and 20s.
micromind is offline   Reply With Quote
Old 12-06-2014, 08:07 PM   #6
Rewards Points: 6
Follow up...Replaced 100 amp breaker and all is fine..Thx for the help,Jack
The Following User Says Thank You to Jack Duren For This Useful Post:
FPE Panel change out. Main Breaber to Lug TJ14u Electrical 4 01-22-2013 10:54 PM
Adding subpanel to Garage jimmyfloyd Electrical 2 11-09-2012 09:22 AM
Main Service Panel to 2 breaker panels - I can imagine you all rolling your eyes kalus Electrical 22 03-23-2012 02:09 AM
Garage Insulation yamster Insulation 0 07-01-2011 01:30 PM
Help with detach garage main feed Holt Electrical 2 10-18-2010 10:44 PM